Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Heating & Air Conditioning (https://www.askmehelpdesk.com/forumdisplay.php?f=150)
-   -   New old crane gas heater 80.000 BTU won't run (https://www.askmehelpdesk.com/showthread.php?t=265817)

  • Oct 2, 2008, 02:37 PM
    bcnelson43
    New old crane gas heater 80.000 BTU won't run
    Hi out there hope someone can help Ive got a crane gas heater in my garage It was never used since bought it was my dads for his garage

    I put it in my garage hug it plumbed gas line from house to garage it has a honeywell
    Thermistat wired I can lite the piot but the main burners won't come on nothing is there anyone that can help Im ready to pull it down and run it over with my truck:confused:


    The id tag says crane company chigago il
    Model CN100-P
    80.000 BTU
  • Oct 2, 2008, 03:07 PM
    hvac1000
    First I believe you will have to make sure your 120 volt supply is good.
    Next make sure the gas valve is turned to the ON position.

    Since we do not know what gas valve is installed on the unit post the brand and model number of the valve so it can be looked up to see what kind of safety device it has. Being it is old there could be a few different ones used.
  • Oct 3, 2008, 06:24 AM
    bcnelson43

    Model # V800 A1005
    Regulator V 5306 A
    Operator V 804 A

    That's what the gas valve has on the side
    I do have 120 to it and the gas is turned to the on position I just can't seem to figure it out hope you can help
  • Oct 3, 2008, 06:27 AM
    bcnelson43
    Opps sorry it's a honeywell brand
  • Oct 3, 2008, 11:18 AM
    hvac1000
    If you do not have a thermostat you will have to add one to control the gas valve. Is a thermostat installed?
  • Oct 4, 2008, 05:56 AM
    bcnelson43

    Yes it's a honeywell heat only thermostat its wire right it came with the heater it only opens and closes the circuit
  • Oct 4, 2008, 10:26 AM
    hvac1000
    If the pilot is lit and the thermostat is calling for heat and the 120 volt power is on and if there is a 24 volt transformer to power the thermostat circuit is generating 24 volts you should have activation of the gas valve. Is the gas valve itself turned to on and not still pointing to pilot?
  • Oct 4, 2008, 06:45 PM
    bcnelson43

    Yes after I light the pilot I turned the knob to run and that's all that happends
  • Oct 4, 2008, 07:19 PM
    hvac1000
    If the thermostat is working and calling for heat and all the other items above are correct it should be working. If not you neeed to backtrack and check each item over till you find the component that is at fault.
    There is no mystery to the system you have. It is the simplest system available today. I do not think the thermocouple is defective because the pilot will not stay lite since the gas valve is 100% shut off style.
  • Oct 4, 2008, 07:53 PM
    MarkwithaK

    While the pilot valve is obviously operating, the main valve could be stuck or just down right faulty. Sometimes you can tap on the valve to get it to open but don't get carried away.
  • Oct 5, 2008, 07:19 AM
    bcnelson43

    The valve was stuck got it to work thanks a lot this heater rock's thanks again
  • Oct 5, 2008, 08:43 AM
    MarkwithaK

    That is a very common issue when a unit has sat without being used for a period. Just like some of us, when you've been off for awhile you don't want to go back to work.
  • Oct 5, 2008, 10:34 AM
    hvac1000
    You might test the safety device that is contained in that old valve since it might be sticking also. Been there done that.
  • Oct 5, 2008, 05:05 PM
    bcnelson43

    I will do just that again thanks for the information and have a great day and weekend

  • All times are GMT -7. The time now is 08:41 PM.