  • Jul 24, 2008, 10:33 AM
    donf
    AFCI Breakers
    For the purpose of discussion:

    Now that the 2008 NEC mandates AFCI breakers be used in new construction, should older breakers be upgraded on an as needed basis. By that I mean if you need to replace a breaker (15 or 20 amp) should you replace it with an AFCI beaker, even though not required by the NEC.
  • Jul 24, 2008, 10:45 AM
    tmentec15
    I would change all of your circuit breakers to AFCI if your house is over 30 years old except you shouldn't change the breaker to AFCI if it had a GFCI outlet connected to it. If your house is under 30 years old, chances are that all of your wiring has been properly but as a backup safety feature it is good to have arc fault protection
  • Jul 24, 2008, 01:07 PM
    tkrussell
    AFCI breakers have been required since at least 2002 edition of the Code on a more limited basis than the 2008 edition.

    You are correct in that replacing a breaker with an AFCI is not required, as the NEC is only for new installations during the period the adopted code is in effect.

    No existing installation is required by code to be brought up to the new code.

    Replacing a defective breaker, or for whatever reason a breaker is being replaced, may be upgraded to an AFCI if desired, however, the installer will need to check the wiring, as older homes were popular with using shared neutrals, which will not work with single pole AFCI breakers.

    Only a couple of manufacturers make two pole breakers that work with shared neutrals, but they are very expensive.

    I live in a home built in 1995, and I will not be upgrading any breakers to AFCI.

    If a customer requests an upgrade, and if the wiring is suited, I will be glad to sell them the job.
  • Jul 24, 2008, 01:30 PM
    donf
    What about a residence with aluminum wiring?

    My niece's residence was done with aluminum wiring and I have already repaired one circuit with an AL/CO snap switch and non oxidant. Would you consider using AFCI breakers given the older aluminum's penchant for arching?

    By the way, I thought that sharing neutrals has always been taboo, thanks for the info.
  • Jul 24, 2008, 02:27 PM
    stanfortyman
    Quote:

    Originally Posted by tmentec15
    ....except you shouldn't change the breaker to AFCI if it had a GFCI outlet connected to it.

    Care to explain why?
  • Jul 24, 2008, 02:44 PM
    Tev
    Quote:

    Originally Posted by tmentec15
    except you shouldn't change the breaker to AFCI if it had a GFCI outlet connected to it.

    That's just wrong, AFCI breakers work perfectly well in conjunction with GFCI outlets. On the other hand if you had a GFCI breaker you shouldn't, in most cases, replace it with an AFCI.
  • Jul 24, 2008, 03:31 PM
    Stratmando
    I know the ARC Fault is required for Bedrooms, Is it, or when is whole house in effect?
    Donf, That I know of, sharing neutrals is Very Commonly used. It is safe, EXCEPT if the Neutral is opened, If you Make good connections, and don't open neutral while both breakers are on, It is safe, and you can have More circuits in a conduit.
  • Jul 24, 2008, 06:43 PM
    Washington1
    For AFCI's the NEC 2008 states: All 120-volt, single phase, 15- and 20-ampere branch circuits supplying outlets installed in dwelling unit family rooms, dining rooms, living rooms, parlors, libraries, dens, bedrooms, sunrooms, recreation rooms, closets, hallways, or similar rooms or areas shall be protected by a listed arc-fault circuit interrupter, combination-type, installed to provide protection of the branch circuit.



    Start,

    It's (The 2008 NEC 210.12) effective when your area chooses or decides to use it.
  • Jul 25, 2008, 06:28 AM
    donf
    Tev,
    AFCI and GFCI provide entirely different services. As I understand it, there are combination breakers available, but they are very expensive.

    You definitely can not use an AFCI breaker in place of NEC mandated GFCI circuits.

    However, I wonder if you can use an AFCI breaker in conjunction with a GFCI receptacle?
  • Jul 25, 2008, 04:25 PM
    Washington1
    Quote:

    Originally Posted by donf
    Tev,
    AFCI and GFCI provide entirely different services. As I understand it, there are combination breakers available, but they are very expensive.

    You definitely can not use an AFCI breaker in place of NEC mandated GFCI circuits.

    However, I wonder if you can use an AFCI breaker in conjunction with a GFCI receptacle?

    -Yeah CH is one company that carries the combo's.
    -Yes you can use a GFCI receptacle on a AFCI circuit.
  • Jul 26, 2008, 10:43 AM
    Tev
    Quote:

    Originally Posted by donf
    Tev,
    AFCI and GFCI provide entirely different services. As I understand it, there are combination breakers available, but they are very expensive.

    You definitely can not use an AFCI breaker in place of NEC mandated GFCI circuits.

    However, I wonder if you can use an AFCI breaker in conjunction with a GFCI receptacle?

    Donf,

    I wrote this...

    "That's just wrong, AFCI breakers work perfectly well in conjunction with GFCI outlets. On the other hand if you had a GFCI breaker you shouldn't, in most cases, replace it with an AFCI."

    I was unclear in my wording. I wrote GFCI outlet but meant GFCI receptacle. Basically, AFCI breakers and GFCI receptacles do work together.

    I know they provide differing protections and would never replace a mandated GFCI with an AFCI. I was trying to say that if there were a GFCI breaker on a circuit where it was not required it could be replaced with an AFCI breaker.

    In short, I apologize if my wording was poorly chosen and will try to be more clear and precise in the future.