    Charging a 2ton unit and the suction line pressure is at 90psi and the liquid line is at 175 psi.new line set,no kines,instill filter on both lines.new air handler and coil.
  • Jul 12, 2008, 09:06 PM
    wmproop
    What is your question,,
    Let me ask one,, why did you install a filter on both lines?
  • Jul 12, 2008, 11:15 PM
    hvac1000
    Possible incorrect metering device.
  • Jul 13, 2008, 06:49 AM
    jspeer22
    Charging a 2ton unit and the suction line pressure is at 90psi and the liquid line is at 175 psi.new line set,no kines,instill filter on both lines.new air handler and coil.

    The unit had been move from the side of the house to back and the lines had been cut with a hack saw so I was told.I hook up a new line set and added both filters for ins.After install I used nitrogen to check for leaks and then vacuum for 1hour.
  • Jul 13, 2008, 07:49 AM
    hvac1000
    The valves in the compressor could be weak. You will have to pump it down to check how it pulls down. Noturally we have no idea what the temp is.

    BTW what is your superheat or subcooling on the system running.
  • Jul 27, 2010, 02:18 PM
    irish_in_pa

    I have a 3 ton unit with a suction pressure of 110 an a head pressure of 190 it's a 10 yr old unit cap tube evap. What could be the problem bad compressor valves?