  • May 26, 2008, 05:32 AM
    webbm2
    From heat to air conditioner
    Heat pump will not switch from heat to ac... help
  • May 26, 2008, 05:49 AM
    hvac1000
    Model number and brand of unit?

    Bad reversing valve
    Bad reversing valve coil
    Check for 24 volts at the coil If present check for coil continuity/OHM if defective replace.

    Valve itself will have to be professionally replaced since it is brazed in place.

    If you replaced the thermostat lately that could also be a problem if not set up or wired correctly.

    Make sure wires going to the outside unit are OK. Dogs/animals chew on them.