I set 2-200 amp panels inside a house and a 320 amp meter base outside am I going to need a meter panel combo for the main panel and use both of the inside panels as sub panels. Right now I have just the meter outside both panels has main breakers
|  | 
I set 2-200 amp panels inside a house and a 320 amp meter base outside am I going to need a meter panel combo for the main panel and use both of the inside panels as sub panels. Right now I have just the meter outside both panels has main breakers
Well, aside from the fact that I can hardly understand your post, I think I get the drift.
Typically I would just use a 320A meter base with double lugs on the load side. Then run two runs of 4/0AL or 2/0CU to the panels.
BOTH inside panels are MAIN panels in this case.
*Quote taken from a duplicate thread.*Quote:
Originally Posted by bonanza 67
This would have been good to know from the start. Yes you will. It will need to be inside where the other main panel is.