Electrical service to detached garage
	
	
		I am building a detached garage and have installed a 125 amp panel.  I plan to install the service disconnect by the meter base.  What size wire do I run from the service disconnect to the panel in the garage.  The distance is about 125 feet.  I have been told that I could use 2-2-4-6 aluminum, but according to NEC Table 310.16 I would need either 1/0 for 90 degrees C or 2/0 for 75 degrees C.  I don't have Table 310.15.B.6, which is what I was told the 2-2-4-6 was selected from.