    Mauro
    100A 240v subpanel with #4 wire
    Hello, I have a 200 Amps main panel and i will install a subpanel 100 feet apart to run my new swimming pool pump, sprinkler pump and garden lights (maybe some other appliances to aliviate load in a 60 Apms existing subpanel)
    Pumps will run in 220v.

    I was told to put 2 #4 wires 1 #6 and 1 #8 on conduit pipe baried 1 feet underground.

    Will this cable work for me? Alcan Stabiloy # 4 AWG S- E- R 4 - WIRE ??

    Also i was told to use a Murray panel 100 AMP.

    Thanks for any help or advice you can provide.

    Mauro
  • Apr 14, 2008, 05:02 PM
    stanfortyman
    Quote:

    Originally Posted by Mauro
    Will this cable work for me? Alcan Stabiloy # 4 AWG S- E- R 4 - WIRE ??

    Not in conduit it won't. Or buried either.
    You need THWN conductors in conduit the WHOLE way since this is a feeder to a pool panel.

    Pools are no place to mess around. Are you familiar with all the codes involved??
  • Apr 15, 2008, 04:03 PM
    Mauro
    Thanks for your reply, I will do it with 3 #4 copper and 1 #6 inside 1" conduit as per my electrician advice.

    Thanks again.