  • Apr 4, 2008, 03:15 PM
    Z280Bill
    Wiring a combination meter and main disconnect.
    I bought a Square D CQRA200 Meter/main disconnect combination and I expected to see the neutral isolated from the ground. Does the neutral and ground start from the same block?
  • Apr 4, 2008, 03:31 PM
    stanfortyman
    Yes, at the service disconnect the neutral is bonded to the case. This is the ONLY place this occurs.