    Wye delta starter
    At 440 volts, What motor rating in KW I will use wye delta starter.
  • Mar 29, 2008, 03:19 AM
    Credendovidis
    Quote:

    Originally Posted by addaddadd
    at 440 volts, What motor rating in KW i will use wye delta starter.

    Star/Delta Starters are required to be fitted on all motors greater than 4KW (about 5 HP).
    The applied voltage is irrelevant. Only the power requirement is the official deciding factor.
    Of course nothing holds you back to install it on any smaller 3 phase motor.
    They are used to reduce the start current applied to the motor during start.
  • Mar 29, 2008, 05:06 AM
    stanfortyman
    Quote:

    Originally Posted by addaddadd
    at 440 volts, What motor rating in KW i will use wye delta starter.

    I have NO idea what you are asking.
    Regardless...


    THIS IS NOT DIY WORK!!! CALL AN ELECTRICIAN!!!
  • Jan 31, 2010, 11:59 PM
    mackycan
    Quote:

    Originally Posted by Credendovidis View Post
    Star/Delta Starters are required to be fitted on all motors greater than 4KW (about 5 HP).
    The applied voltage is irrelevant. Only the power requirement is the official deciding factor.
    Of course nothing holds you back to install it on any smaller 3 phase motor.
    They are used to reduce the start current applied to the motor during start.

    As for me, I recommend him to use wye-delta starter for 7.5hp and higher. For < 7.5hp just use CB and inverter, or cb and contactor (you can't vary the speed though)...