Originally Posted by speedball1
"would it be code??" No, Code calls for a 2" drain to be vented not over 5' from the trap. At 10' you're way outta code. I can see why you'd want to connect to the kitchen drain but choking the flow down from 2" to 1 1/2" at the connection isn't the best of ideas. You're setting up a restriction that rotting hair matted with grease can build up as a clog. Your choicebutsince you're gonna hafta vent the shower anyhow I would look for a better connection. Let me know what you decide. Tom