  • Dec 5, 2007, 07:05 PM
    honeywellEW07
    Blowing fuses
    Had new thermostat installed,most everything on this york unit has been checked,couldn't find a problem,boards,contacts,relays all checked out to be fine,still blowing 5 amp fuse when calling for heat??
  • Dec 5, 2007, 07:17 PM
    Stratmando
    Remove wires to heat contactor coil, if it blows, maybe shorted windings. Also verify no load when coil(control) wires are removed. White wire is sometimes used for heat.