Ehaust requirement on a 90%+ gas furnace
	
	
		I am installing a Heil 90%+ 100,000 furnace and I'm told that I must have a 3" PVC flue. The intake and exhaust are both 2" and the installation manual doesnot say where the 3" is to start and end. To get the the outside wakk is less than 15 feet and has to have 2 long 90's and 3 45's in the run. all this accure in the first 6 feet. The straight run from there is 10 feet. If I run only 2" the distance the draft switch will not close. One HVAC mech told me all I have to install is a section of 3" in the run and finish with 2" comb intake/exhaust fitting through the plate to outside. Thank you for your time, Don
	 
	
	
	
		Comment on tsa7man's post
	
	
		Thank You this solved the problem. The book was not in the furnace.