Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Heating & Air Conditioning (https://www.askmehelpdesk.com/forumdisplay.php?f=150)
-   -   HoneyWell Thermostat Wiring RTH230 (https://www.askmehelpdesk.com/showthread.php?t=150916)

  • Nov 11, 2007, 03:15 PM
    sabfk
    HoneyWell Thermostat Wiring RTH230
    Hi,

    I am trying to install a HoneyWell RTH230 programmable thermostat to replace our old Honeywell round thermostat. I have a Miller gas furnace and electrical central air. The wiring to the old thermostat was as follows:

    Red
    Orange
    White
    Yellow
    Green

    There were also blue and black wires coming out of the wall but not hooked up to the thermostat.

    I hooked up the new thermostat as follows:

    Red to Rh
    Orange to Rc
    Yellow to Y
    Green to G
    White to W

    And left the blue and the black ones unattached. The heat seems to be working fine but I cannot get the AC to come on? Any ideas?

    Thanks for your help.
  • Nov 11, 2007, 07:18 PM
    hixton
    Disconnect the orange and put a jumper between rh &rc you should be fine ac should work
  • Nov 11, 2007, 07:35 PM
    labman
    If that doesn't work, check what the orange is connected to at the furnace. You may want to look at the sticky at https://www.askmehelpdesk.com/heatin...ons-58313.html