-   -   Goodman furnace will not start (https://www.askmehelpdesk.com/showthread.php?t=145996)

  • Oct 28, 2007, 05:19 PM
    DarkCloud
    Goodman furnace will not start
    Newer goodman furnace will not start on call for heat... well 1 out of 15 times it will. The little fan turns on , the HSI glows , gas valve clicks after HSI goes out. This is LP. Can Anyone help?
  • Oct 28, 2007, 07:35 PM
    wmproop
    Is there gas,, could it be turned off
  • Oct 29, 2007, 01:05 PM
    DarkCloud
    NO the gas is not turned off
  • Oct 29, 2007, 02:30 PM
    acetc
    There is a safety pressure switch located close to the gas valve to shut it off in case of low gas pressure, this switch is only installed on propane furnaces. Check you gas pressure with a manometer, the proper pressure will be on the data tag on the furnace. Good luck, Mike