    Furnace Reseting over and over
    I have a white Rogers system that When turned on doesn't cycle up and turn on It starts for about 1-2 seconds then resets over and over I have tried cleaning the flame rod and also change Thermastat and ignitor. Any idea what would cause this?
  • Oct 12, 2007, 04:58 PM
    acetc
    Sounds like possibility an ignition control modual.
    Do you have a good blue flame or is it yellow?
  • Oct 12, 2007, 06:56 PM
    T-Top
    Make sure you have a good equipment ground on the ignition control box and on some systems the gas valve has to have a good ground to the equipment also. Or if the flame sensor (the metal rod part) is touching the burners or any other metal it won't work. Make sure flame sensor wire has not grounded out to equipment also.