Originally Posted by Washington1
What Load! You said you did not add anything to the new wire from the Garage GFCI. (Sorry to hear that the bath is on the same circuit. By today’s standards that's a code violation. Also, It would be best to dedicate the backyard branch, so you can avoid any future tripping--due to the fact that the garage and bath are all on one circuit.)
Check the wiring connection at the GFCI, and make sure all your wire terminations are correct (Power-in to line side. Newly added wire to load side of the GFCI). If all is correct, undue the newly added wire, and reset the GFCI. If it resets, give it some time and see if it trips in the same amount time of its last trip. If it doesn't trip, then you have a problem somewhere on the new wire: Neutral or hot to earth or ground. If it does trip, then this tells you that the wire added is not the cause--which means you will have to start checking all dead outlets (outlets with no power). Check everything that’s not working on that circuit. [Also note that tripping can be caused by defective items plugged into outlets related to the dead circuit. Unplug these items, then plug them back in one at a time, and see if it trips the GFCI. Lastly, it could be a defective GFCI.]
This is a troubleshooting task, so it takes time.
If missed anything, it's because I'm 1/2 sleep :)
No 240v GFCI needed.
What are you planning for the new wire?
Get back to us on your results!