    cafehyde
    Double tap on neutral feed
    Hello,

    I noticed that my neutral feed wire in my panel is tapped under it's connection lug with another neutral feed going to a sub panel. Is this troublesome? If so, what could be hazardous about it?

    Thanks ahead of time.

    Eric.
  • Jul 11, 2007, 02:26 PM
    tkrussell
    Most lugs are only rated to handle one conductor. There is a potential for a loose connection developing, which can cause heat and damage the lug, wire, and lug mounting.

    Getting a loose neutral is the worst case, as loose shared neutral will cause abnormal voltages to be impressed on branch circuits.

    You can take both wires off and splice together with a short pigtail to the lug. Power needs to be off, and the mechanical connector needs to be able to handle three wires of the size you have.
  • Jul 11, 2007, 09:48 PM
    KaFidela
    Quote:

    Originally Posted by cafehyde
    Hello,

    I noticed that my neutral feed wire in my panel is tapped under it's connection lug with another neutral feed going to a sub panel. Is this troublesome? If so, what could be hazardous about it?

    Thanks ahead of time.

    Eric.


    If the connection lug is "type Y" and can handle 2 conductors or if the connection lug is bigger than the size of 1 conductor and can fit 2 conductors, I think it's safe as long as the lug is crimped and fastened properly in the neutral terminal in the panel.