    New Amana heat pump system: outdoor unit ASZ140481A, indoor unit (in attic) AEPF426016B + TXV. Thermostat: TotalTouch P286-200.

    When fan setting is FAN AUTO and the system is not cooling or heating, the fan can come on and stay on for hours, or the fan stays on after heating/cooling stops. The fan used to be on (hours or days) and off (hours or days) but now it seems to be on all the time. The speed used to be various and now seems to be high all the time.

    The guy who installed the system replaced a circuit board in the indoor unit, but the problem persists. He thinks the thermostat works fine.

    How can the fan be on when it should not? What to check (other than the circuit board)?

    Thank you for your help.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Jun 8, 2007, 08:07 PM
    That unit has a variable speed motor I believe. You better find someone with the proper tester for that GE motor. It could be a problem on the end bell of the motor or circuit board not set up correctly.
    fanstayson's Avatar
    fanstayson Posts: 2, Reputation: 1
    New Member
     
    #3

    Jun 14, 2007, 07:53 PM
    Quote Originally Posted by fanstayson
    New Amana heat pump system: outdoor unit ASZ140481A, indoor unit (in attic) AEPF426016B + TXV. Thermostat: TotalTouch P286-200.

    When fan setting is FAN AUTO and the system is not cooling or heating, the fan can come on and stay on for hours, or the fan stays on after heating/cooling stops. The fan used to be on (hours or days) and off (hours or days) but now it seems to be on all the time. The speed used to be various and now seems to be high all the time.

    The guy who installed the system replaced a circuit board in the indoor unit, but the problem persists. He thinks the thermostat works fine.

    How can the fan be on when it should not? What to check (other than the circuit board)?

    Thank you for your help.
    Thanks. The problem was loose connection to the motor (from the circuit board).

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

A/C unit fan stays running [ 2 Answers ]

The FAN on the air conditioner unit on top of my house stays running all the time. The unit cools when it is supposed to, however when it's reached the room's temp, and the house thermostat automatically shuts of the unit, the fan staysd on. It even stays on when the slide switch on the thermostat...

A/C Fan or Blower doesn't come on ! [ 5 Answers ]

Hi, One day I turned on the a/c, noticed my house is not cooling down, and found out that the fan is not on. I can hear the motor and the compressor running. I have the capacitor replaced but the fan still won't come on. Could anyone tell me what is wrong with my a/c? Thanks you !

Fan Blower doesn't come on in Fan,heat or cool [ 2 Answers ]

Yesterday I turned on my heat(coil in air handler) and everything worked fine. Last night I turned it on again and the fan wouldn't come on no matter where the switch was: fan only, heat or air. I made the appropriate temp changes for heat/air. There is a humming noise coming from the heating coil...

Heat won't come on and blower stays on all the time. [ 1 Answers ]

I have a problem with a furnace that the heater won't come on, "not at all", and the Blower it stays running all the time, can't turn it off unless disconnected. Before replacing the Circuit Board, I will appreciate if somebody tells me what other reasons are there that may cause this problem. ...

Blower fan [ 1 Answers ]

When icut my heater on the heater work okay but the fan wouldn't go off when it warm up