    Panel Circuit Breaker
    I live in a four bedroom colonial. The Pacific Electrical Panel is 125amps and 29 circuit breakers of which 3 are not in use. Is it necessary to upgrade the system to 200 amps? I have no problems with it and is seldom overloaded. If I choose to upgrade the panel what is the cost of such a project.
    Anthony_'s Avatar
    Anthony_ Posts: 38, Reputation: 1
    Junior Member
     
    #2

    May 26, 2007, 07:43 AM
    When you say it is seldom overloaded, do you mean the main breaker is overloaded and tripping? Or individual circuits?

    It's not necessary to upgrade unless there is a need for it, like if you are doing some adding on to your house or adding a hottub or a garage with some welding equipment and the service you have is not enough. If you don't plan on adding anything, your 125 amps should be fine.

    If you do decide to upgrade the price can range from $1000 to $1500. Get a few quotes from reputable contractors in your area.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #3

    May 26, 2007, 07:44 AM
    If your 125 Amp trips, 200 Amp not a bad option.
    200 Amp disconnect, and breaker,
    2" conduit from disconnect to panel.
    2-2/0 wire for Hots.
    1=1/0 wire for neutral
    1-#4 for ground
    40 circuit Panel, Main Lug
    Breakers
    Prices vary in areas, take list to local supplier and length of Wire and PVC needed
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    May 27, 2007, 07:31 AM
    Should you decide to ask contractors for an estimate, ask that they do the service calculations to determine if a larger service is needed, and what size service would be required.

    While you may need to pay a service call charge for the calcs to be done, a small investment to be sure your service is sized properly, rather than guessing.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Main Circuit Panel to Branch Panel? [ 1 Answers ]

Hello experts, OK... My Main Load center in my home has a branch circuit connected to a 60 amp breaker. The branch feed wire is a 4awg copper wire. The branch panel is downstairs and it has a 100amp main cutoff breaker installed in it. It feeds the whole downstairs including... (1)...

Circuit breaker [ 3 Answers ]

A circuit breaker connected to the kitchen tripped twice. I had an electrician in but the problem persists - in fact, the very day the electrician came. It does not seem to be caused by any one particular appliance. The first time I was using the waste disposal and the next two times nothing was...

Replacing a circuit breaker with a GFI breaker- q on neutrals [ 1 Answers ]

In process on installing withquestion on neutral wires. Do you take the neutrals out of the in the main panel neutral and put them in into the breaker where its labelled "load neutral terminal" and only have the neutral "pig tail" to the panel neutral bar? Thanks!

Circuit Breaker [ 1 Answers ]

I have 14 gauge electrical wiring with a 15 amp circuit breaker can I change that circuit breaker to a 20 amp. Thanks Michael:D

Breaker panel [ 1 Answers ]

Can I use a 200 amp box with 100 amp service


View more questions Search