    J Bone's Avatar
    J Bone Posts: 15, Reputation: 1
    New Member
     
    #1

    May 9, 2005, 07:56 AM
    Bathroom Wiring
    I am in the process of putting in a full bath and had a question regarding the wiring. I ran a #12 and #14 from the breaker and intended on using the #14 for the bath fan/lights and the #12 for the GFI outlet.


    I want to also run the 12 gauge from this GFI to one I intend to install in the upstairs bathroom in about a year when I remodel it. It would seem OK to have both outlets on the same 20 amp circuit since these 2 outlets will be the only devices on the circuit, plus rarely if ever will both outlets be used at the same time (for example, unless we have guests and 2 women are using hair dryers at the same time).

    Is this OK to do, or should I run another circuit for the upstairs bathroom?

    I also want to do the same with the bath fan/lighting, and use the same circuit if possible... Please advise

    Thanks
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #2

    May 9, 2005, 05:20 PM
    I don't see a problem. You can use the feed through feature and have GFI service from a regular outlet in the second bath. Often there are little stickers to put on the other outlets feeding off a GFI one.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    May 9, 2005, 05:40 PM
    According to code, all bathroom outlets must be a 20 amp circuit, with #12 wire, and dedicated for the bathroom outlet(s) only, and must be GFI protected.

    As labman mentioned, you can incurr the cost of only one GFI device in the lower bathroom, and using the feed through terminals on the GFI outlet, protect the upstairs bathroom outlet.

    Each new device you purchase must have labels " GFI Protected" to apply to standard outlets which are GFI protected from a GFI device upstream. Use the label to inform a user that they are safe to use the outlet,which if in a bathroom, will most likely be next to a sink.

    There is no limit as to the quantity of bathroom outlets that can be connected to this dedicated bathroom outlet circuit,(however, if you are Bill Gates with 25 bathrooms in the house, you may want to consider installing more circuits, that is hoping you did not blow the budget on gold fittings and floor to ceiling marble)

    Chances are nil, but possible that both outlets are used at the same time with hairdryers.


    And you can use the other 15 amp circuit to feed the fan light units in both bathrooms. I caution you that if any fanlight unit is in or above a tub or shower area, the fan light must be GFI protected also, and not connected to the outlet GFI, must have its own GFI.

    Hope this helps, Wire Safe!
    jasv's Avatar
    jasv Posts: 35, Reputation: 2
    Junior Member
     
    #4

    May 10, 2005, 11:28 AM
    Thanks for the detail
    I am also remodeling a bathroom and decided to add a light/fan over the shower. I had not thought of GFI protecting it. Do I need to have a GFI circuit breaker or will a GFI outlet upstream do?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #5

    May 10, 2005, 02:17 PM
    You can always use a GFI breaker, but they are expensive, I think about 40 dollars at the box stores.


    There is also a device that mounts like an outlet, but does not have the receptacle holes, called a deadfront,or blank GFI. You can mount in a box next to the wall switch, if you use one switch you will need a 2 gang box to hold both the switch and the deadfront GFI, and wire it just like a receptacle.

    I think they are about $15.00, and you benefit by having the GFI in the room you will use it for access to the test and reset buttons.

    Breakers are great, but if it trips, you need to drag yourself to the panelboard.

    And you can either use one to protect the bathroom fan in that room, and either wire it to protect another devices upstream or wire so upstream is not protected.

    Now in this case the outlet that must be GFI in the bathroom can also protect the fan light. This can be the simplest way, but the downside to this, if the GFI trips, you lose both the outlet and the fan light.

    So now you have several options. Any further questions on thes let me know
    ATTITUDEDA's Avatar
    ATTITUDEDA Posts: 2, Reputation: 1
    New Member
     
    #6

    May 16, 2005, 07:34 AM
    Confussed
    Can soneone explain why the fan or light can not be connected to the same GFI outlet. Is there a difference between adding an extra outlet to a GFI vs a light or fan. Thanks..
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #7

    May 16, 2005, 04:07 PM
    Not sure where you are getting the fanlight cannot be connected to the GFI in the bathroom.

    Below is an excerpt from my last post to jasv:

    "Now in this case the outlet that must be GFI in the bathroom can also protect the fan light. Thsi can be the simplest way, but the downside to this, if the GFI trips, you lose both the outlet and the fan light."

    The code reqiuers an outlet be installed in a bathroom nxet to the sink, this outlet must be GFI protected, and must be a dedicated 20 amp circuit for bathroom outlets only, however does allow for other devices in the bathroom that need GFI protection be connected to this bathroom outlet circuit.

    Have I help clear this confusion up for you? If not get back to me and we can discuss further.
    ATTITUDEDA's Avatar
    ATTITUDEDA Posts: 2, Reputation: 1
    New Member
     
    #8

    May 17, 2005, 03:35 AM
    Thanks I must of read your post wrong the first time.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Bathroom wiring diagram [ 8 Answers ]

I am wiring a new basement bathroom. I have created a diagram showing how I plan to wire it. Just curious if anyone sees any problems with the way I'm doing this? Thanks and hope the attachment shows up correctly!

Another Bathroom is needed... The boys are fighting to use the bathroom [ 7 Answers ]

First, thank you for having this kind of forum. Now also let me say that I'm not well versed in the plumbing lingo so hopefully you will be patient with my questions. I live in a 3 levels home (Basement, Main, Upstairs) with the existing bathroom is on the main floor. I'm planing to add...

Bathroom light + extractor fan wiring [ 1 Answers ]

I am about to replace the light fitting in the bathroom, but the extractor fan is connected to it, there is a number of wires which are all connected, with only 2 brown wires coming down, but I have 3 connections on my new light fitting -earth, live, neutral, how do I connect it properly?...

Bathroom wiring [ 2 Answers ]

First question was answered somewhat,here's the scenario,remodeling bathroom,ran 20 amp service,wired in fan/light .light is wired for use by itself.Fan,light in tub,shower,vanity light and three outlets [one outlet is gfci,20 amp rating. Would like to use 15 amp switch for general light,this is in...

Bathroom [ 1 Answers ]

I have two bathrooms in my home, one has a shower and the other bathtub. The shower has been stopped up for a long time now... the water was going out slowly now it doesn't go out at all... recently the tub in the other bathroom has stopped up same thing... the water was going out slowly, and now...


View more questions Search