    Payne Heat Pump loose fitting
    My Payne heat pump was installed August 2003. Noticed a few months ago that it would run constantly. Had it checked out. Repairman said it was leaking through the flare fitting. My question is: If a flare fitting was tighten three years ago can it jiggle loose on its own, because of the vibration when it runs?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    May 16, 2007, 01:02 PM
    Normally a Flare fitting is as good as the flare it is made up of. Usually you have to use a special flaring tool to make up the flare. Where some people mess up is when the fitting is large like a 5/8 or 3/4 or 7/8 they forget to put oil on the male part of the flare threads. Without the oil the flare is harder to tighten down to make a good seal and can eventually back of just enough for a small leak.

    Vibration can also cause a leak especially if no oil is used during assemble.
    If the fitting flare assembly is cocked or put under stress just a bit during assembly that can also cause a problem.

    I prefer to braze my refrigerant connections but there are a few companies that use a flare. One nice thing about a flare is the you do not take the chance of burning up the valves at the condensing unit while brazing.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Heat Pump - Payne [ 4 Answers ]

Hi. I sent a request to Carrier regarding my question but they want to send a service rep. instead of answering my question. I have a one year old heat pump that was added to my medium efficiency furnace. I live in Canada, West Coast, and the heat pump will now not continually provide cool air. It...

NO HEAT! Janitrol heat pump and AC system. Changing to Lux Thermostat. Wiring issue. [ 11 Answers ]

I have a Janitrol A/C and heat pump system. I replaced the thermostat with a Lux T9000LC The A/C works fine, but the heater does not. I have it wired as follows: G - Green Y - Yellow W - White RH - Pink B -

Heat pump stuck in heat mode [ 4 Answers ]

I have a heat pump that seems to be stuck in heat mode. When you try to turn the a/c on it runs heat. I got the a/c to run by cycling the power a couple of times but after having to use the heat again, it is stuck again. Could this be an electrical problem or is it probably the reversing valve?

Electric heat pump auxilery heat problem [ 4 Answers ]

Equipment: Trane XL1400 4 years old Auxilery heat: Strips... 2 -60Amp circuits Filters changed every 30 days I cleaned outdoor unit summer 2006, as every year. Thermostat: Honeywell Chromotherm II Problem: I have been noticing at times the aux heat kicking in at times I think it should not....

Heat pump vs electric heat [ 3 Answers ]

I have a heat pump with a two stage thermostat, 1st stage is heat pump, 2nd stage is electric (resistance) heat. Is it ever more economical to run the furnace with resistance heat only, not the heat pump? I know that the outdoor temperature affects the ability of the heat pump to work, but is...


View more questions Search