    How to tighten Main Lugs in panel to proper torque
    The Square-D panels I'm using have a hex nuts that can only be tightened with an hex tool (aka allen key/wrench). There is a 50 lb/ft suggested torque specification for this nut. I have torque wrenches for normal sockets but not for a hex nut.

    Wonder if there exists a special torque wrench (or an attachment) to tighten hex nuts?

    Thank
    -kd
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    May 15, 2007, 02:28 AM
    If you have a typical 3/8" drive torque wrench, the socket you need has a fixed Allen wrench attached to a socket, such as shown in the picture. Nothing special, just an attachment not see often.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Difference between Main Lug and Main Breaker Panel [ 8 Answers ]

What is the difference between a Main Breaker Panel and a Main Lug Panel and can either be used in new residential construction.

Main Panel to Sub Panel [ 2 Answers ]

I currently have a CH MBE4040B200BTS Meter main panel on my pump house drawing only power to run booster and well pumps, here is what I wish to do: Add a CH BRS225 (feed thru) to a CH BR4040B200 Main Breaker sub panel for my shop. Both panels are only 200 amp service, I will not be running more...

Main Circuit Panel to Branch Panel? [ 1 Answers ]

Hello experts, OK... My Main Load center in my home has a branch circuit connected to a 60 amp breaker. The branch feed wire is a 4awg copper wire. The branch panel is downstairs and it has a 100amp main cutoff breaker installed in it. It feeds the whole downstairs including... (1)...

Main panel as subpanel [ 2 Answers ]

Hello: I stumbled across your forum and found a question that was close to mine, but have a more detailed query. I am wiring a shop/apartment. The building has a 200 amp service panel. The main loads (a/c, range) and dedicated loads (fridge, smoke detectors, etc) are branch circuits on the main...


View more questions Search