    Rheem heatpump contactor not energizing
    I have a heat pump that is not energizing when the tstat calls for cool (or hot). I'm getting 24V to the circuitboard (yellow in from tstat to common), but not across the control terminals of the contactor. Manually pushing the contactor down starts the fan and compressor and the system appears to work fine.

    It seems likely that I have a problem with (a) the coil, (b) the circuit board, or (c) the "other little black box" (reversing valve?). Am I on the correct path, and if so, could someone please suggest an appropriate troubleshooting procedure to track down the faulty component.

    Thanks,
    -Tim
    hvacservicetech_07's Avatar
    hvacservicetech_07 Posts: 1,083, Reputation: 75
    Ultra Member
     
    #2

    May 4, 2007, 09:29 PM
    What model is the heat pump? The little black box? Is it next to the contactor? It may be a time delay relay... Do you have 24 volts on any terminals outside?
    hvacservicetech_07's Avatar
    hvacservicetech_07 Posts: 1,083, Reputation: 75
    Ultra Member
     
    #3

    May 4, 2007, 09:32 PM
    It could be many different problems... Newer heatpumps have several safety devices, I would start with making sure it's not the loss of charge switch. Again I need to know if you have 24 volts anywhere on the heatpump?
    tbrent2000's Avatar
    tbrent2000 Posts: 2, Reputation: 1
    New Member
     
    #4

    May 5, 2007, 12:16 AM
    OK, I found this similar post and it looks exactly like the problem I am having (you also worked on this one hvac):
    May 2, 2007, 06:38 PM
    Cnyle
    Compressor Contactor chattering?
    ----

    Of course, my contactor is not chattering, but rather not engaging at all.

    I'll be checking the wiring to the inside unit for continuity in the morning if necessary, but as I mentioned before, there are 24V at the circuit board, so I think the problem is in one of the components in the control area. I'll also jump the control leads on the contactor to make sure the coil is pulling.

    As far as the model, I'll have to get back to you on that tomorrow.

    Please help me understand the components in the control area and their general function / relationship. If I'm standing at the front of the unit, this area is a box with weatherstripping to the right of the fan / condenser housing. Part of the access panel forms the top of the box by sealing against the gasket. On the far left side of this box is the contactor (sitting roughly above the main capacitor). On the right side, from back to front is a coil, the circuit board (mounted vertically on the right wall of the box), and this other black box (mounted vertically on the front wall of the box). It sounds like this latter control is a time-delay relay based on the above thread.

    Let me know if this description is not useful and I can send a pic instead.

    Thanks for your help.
    -Tim
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #5

    May 5, 2007, 08:31 PM
    Check the high pressure switch. Red button bottom of the heatpump just above or bellow the freon lines(out side of the unit) push it in, it's a manual reset for the high pressure switch. Good luck let us know what happens.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Compressor Contactor chattering? [ 13 Answers ]

Hello all, I have been trying to find out some answers for my cooling problem. I have a Rheem A/C unit that as of yesterday has worked fine. When I switch my theromstat to cool I get the blower to start, but the outdoor unit will not fire up. I replaced the compressor contactor hoping that was...

Distiguish between contactor and circuit breaker ? [ 1 Answers ]

What is difference between contactor and circuit breaker ?

Contactor replacement on Home Condenser [ 2 Answers ]

Hello, My outside Condenser is not kicking on. Air Handler and thermostat OK indoors. I checked the Contactor and it looks extremely dirty and pitted although not fused together. If I hold down contacts manually, Condenser / fan etc. starts and is blowing cold air. Once I release Unit stops...

Am I being duped by contactor? [ 1 Answers ]

Im not sure if this is the right place fore this post... but here goes. We bought this house in September. It was a new home built on an existing foundation (old home burned down). Now normally I have been told of the "settling" that's to occur, But should everyjoint in the home be literally...


View more questions Search