    Oil burner circuit
    I have an oil burner and want to add and air conditioner unit,do I need a second 24v thermostat for the cooling circuit
    ebaines's Avatar
    ebaines Posts: 12,131, Reputation: 1307
    Expert
     
    #2

    May 4, 2007, 06:11 AM
    You're adding an AC unit to the existing system - i.e, you have a forced hot air system, correct? Doing this work will require substantial revamping of the furnace - have you considered going w/ a complete upgrade, i.e. replacing the old furnace w/ a complete new heating and AC unit?

    Well, to answer your question - yes, a single thermostat can control both heating and cooling, but they typically require a 3-wire circuit. So if the thermostats in your home have a 3-wire cable coming to them you will simply need to replace the heating-only thermostat with a new heating/cooling one. If you only have 2 wires (which is what I bet you have), then you will need to run a new cable from the heater/AC unit to the thermostat.
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #3

    May 4, 2007, 06:42 AM
    Depending how old your system is, for the controls, you may need to do no more than run a pair of wires from the furnace out to the new A/C. You may need to replace thermostat and run a 4-5 wire cable. The big question is does the blower have the capacity for the higher air flow an A/C requires. At least part of the A/C installation must be done by a licensed technician. It will include adding an ''A'' coil to the furnace. Ask several contractors to give an estimate. They will know what to look for as far as your current system.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Oil Burner still dripping.Oil Co. Tricks.fear for 3 dogs lives [ 8 Answers ]

That 1 you see as a response to my boiler question was to redirect my boiler question to heating and cooling. Please refer to boiler burner dripping below. Still need an answer as am not willing to have the tricky oil companies service my problem after causing it. They want to see more dollars...

Boiler Dripping heating Oil from directly under burner [ 3 Answers ]

I have an oil burning boiler for hot water heating of home and for hot water usage. It is a New yorker S-97-AP. The burner model AFG UL AJ-737635 has developed a constant drip of about 3 tablespoons every 12 hours. This all happened after a service inspection of my furnace and an oil delivery....

Oil furnace, Burner cuts out [ 4 Answers ]

Ok, my original post was over a noisy draft regulator. Since then I have determined the cause of the regulator banging was the burner going out. This only occurs for a fraction of a second, just little pulses. I changed my in-line fuel filter and my burner nozzle. When I remove the inspection cover...

Oil burner Blower cycling on and off [ 2 Answers ]

Just finished with a new second floor addition. Upgraded to two zone heating from single zone. When heat comes on after expected delay for temp to rise the blower comes on for fifteen seconds then kicks off and comes on again in about two or three minutes, and kicks off again in fifteen seconds, on...

Oil Burner Furnace [ 1 Answers ]

The problem goes like this. Thermostat calls for heat, burner starts and runs for a minute or so and shuts off. After burner shuts off, the blower starts and the burner starts again until the thermostat reaches temp and the burner shuts off blower contiues to run until the low temp limit is...


View more questions Search