    My oil burner will not fire unless I turn the service switch off then back on
    I have a Weil Mclain oil burner hydronic heating system with Aquastat L8124 and R8184 primary. The system will run fine for several "call for heat" cycles but then fail to fire upon a call for heat. When this happens, the red reset buttons on the primary and on the motor DO NOT popup. Upon simply turning the service switch off then on, the burner fires. What could be causing this?
    Also note that I initially had an old Honeywell "dial type", two-wire thermostat and this condition was occurring. I changed to a new digital thermostat and the condition still occurs.
    talaniman's Avatar
    talaniman Posts: 54,325, Reputation: 10855
    Expert
     
    #2

    Dec 14, 2017, 06:48 AM
    Many of these boilers have a stage delay, or a boiler delay. This delay prevents short cycling when different zones call for heat. Review your manual and check your set points and maybe get a tech to tweak those settings. Are you getting any discharge at the relief valve? Monitor it for a few days. The next time your burners don't fire TIME it instead of resetting it. A delay of 3-10 minutes is not at all unusual after several heating cycles, longer may indicate adjustments.

    Another thing that comes to mind is your service maintenance. Just from the point of efficiency how often are your burners cleaned? When was the last time? Every fire up and flame out builds up soot residue in oil fired burners. Talk to your tech or service guy about this before you go about any tweaking yourself is my recommendation.

    I highly suspect YOU are the cause of this condition.
    Monitoring your system and learn the nuances of electronic heating controls is indicated. Let me know what you find.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

When I turn off the gas switch blow comes on then turn switch back on furnace works. [ 1 Answers ]

When I turn off the Honeywell gas switch comes on then pilot lites one time furnace runs for 3 min shuts off an sits, until I do it again.

Why Does Gas Furnace ignight main burner go on then turn back off [ 0 Answers ]

Call for heat,ignighter lights,main burner lights, all turns off, retries 2 more times then blower comes on blowing cold air

Furnace will not fire up the burner. [ 0 Answers ]

Thermostat is OK. There are 24 volts to transformer. Pilot is lit. Furnace is ignition type. There are three wires to Honeywell gas valve. Measured voltages between all three wires. Could gas valve be bad. What else should I check .

Burner does not fire up when heat turned on [ 3 Answers ]

Hi, I have a Lennox Furnace, when you switch on the thermostat to heat and adjust the temp. accordingly, the burner does not ignite. Pilot flame is working, fan works. But no flame on the burner. Here is how the thermostat is wired (Is it right? ) RC- blue wire, G- black wire Y- red wire W-...


View more questions Search