New Member
|
|
Jun 16, 2016, 06:19 AM
|
|
Outlet keeps tripping
I'm trying to get power to my pool. I made a cord with 10-2 plus ground wire. It is plugged into a 110 outlet and run is 85' to a box with two ground fault outlets. One outlet is grounded other is grounded to box but box is not grounded yet. The ground fault outlets keep tripping and every time I reset they just trip out again. I have checked and they are wired correctly. Please help
|
|
 |
Home Improvement & Construction Expert
|
|
Jun 16, 2016, 07:48 AM
|
|
GFI outlets do not have to be grounded to work.
If the outlets keep tripping that means you have a short between the hot and neutral. A very minor short, not enough to trip the breakers. If they trip with nothing plugged into them that means that the short is in the wiring. If they trip when you plugged something in, that means the short is in the thing you plugged in.
Plug your extension cord into another outlet and see if the GFIs trip. If they do that means that the fault is in the extension cord that you made. If they do not trip that means the fault is in the wiring before the outlet you are using.
|
|
 |
New Member
|
|
Jun 16, 2016, 09:05 AM
|
|
 Originally Posted by hkstroud
GFI outlets do not have to be grounded to work.
If the outlets keep tripping that means you have a short between the hot and neutral. A very minor short, not enough to trip the breakers. If they trip with nothing plugged into them that means that the short is in the wiring. If they trip when you plugged something in, that means the short is in the thing you plugged in.
Plug your extension cord into another outlet and see if the GFIs trip. If they do that means that the fault is in the extension cord that you made. If they do not trip that means the fault is in the wiring before the outlet you are using.
Can it be because of more then one ground fault outlet
|
|
 |
Uber Member
|
|
Jun 16, 2016, 10:33 AM
|
|
You have a shared or split neutral. Did you wire one off the load side of the other? Won't work that way. You need 2 line feeds, not line and loads. You can load feed non GFIC outlets.
|
|
 |
Printers & Electronics Expert
|
|
Jun 16, 2016, 10:37 AM
|
|
There are very strict codes regarding the use of electrical circuits near pools.
So let's start this way, how close to the pool are these receptacles?
You said you made the extension cord using 10/2 with ground, correct, did you put a plug at both ends of the cord? Or a receptacle at one end and a plug at the other?
If the GFCI keeps tripping, then you need to make certain that the extension cord is not the problem. The GFCI is designed to protect people from getting shocked. It will trip if it senses a 6 ma difference in current between the neutral (white) and source (black). Also, I do not believe that you should be using a self made extension cord anywhere near a pool.
|
|
 |
New Member
|
|
Jun 16, 2016, 11:05 AM
|
|
 Originally Posted by donf
There are very strict codes regarding the use of electrical circuits near pools.
So let's start this way, how close to the pool are these receptacles?
You said you made the extension cord using 10/2 with ground, correct, did you put a plug at both ends of the cord? Or a receptacle at one end and a plug at the other?
If the GFCI keeps tripping, then you need to make certain that the extension cord is not the problem. The GFCI is designed to protect people from getting shocked. It will trip if it senses a 6 ma difference in current between the neutral (white) and source (black). Also, I do not believe that you should be using a self made extension cord anywhere near a pool.
It is about 10 feet from pool and has plug on one end and receptacles on the other
 Originally Posted by creed1176
It is about 10 feet from pool and has plug on one end and receptacles on the other
I'm using a 10-2 direct burial wire
|
|
 |
Ultra Member
|
|
Jun 17, 2016, 05:31 AM
|
|
Did you read about the Aztek motel in Wildwood, NJ last week?
Electricity and a pool can be a fatal combination. Please don't guess
or try to save a few bucks by cutting corners. Hire a licensed (and insured)
electrical contractor and do it right.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
GFCI outlet keeps tripping
[ 9 Answers ]
I just moved into a new house and I have a GFCI outlet in my garage that has become problematic. It controls the lights and fan in my master bath and 2nd bath, as well as the outlet at the front of my house. There is also an ADP security system tied to it. The problem I have is it keeps tripping....
GFI Outlet keeps tripping
[ 1 Answers ]
My outdoor GFI outlet keeps tripping. I think it could be faulty wiring. I just bought the house so I am still learning things about it. I went to test one strand of xmas lights and when I wiggled the cord in the outlet the reset button popped out. I reset and hung all my xmas lights and everything...
GFCI Outlet Keeps Tripping
[ 4 Answers ]
I have a GFCI outlet that keeps trippping. We've been in this house for years and have never had this problem. We don't have any additional appliances/lighting etc. running on this circuit or anywhere in the house for that matter.
It keeps tripping after reset; sometimes immediately sometimes...
Outdoor electrical outlet keeps tripping gfci outlet
[ 3 Answers ]
Until just recently my christmas decorations would light up when we plugged them into the outdoor electrical outlet. Now when we plug it in the gfci outlet in the garage keeps getting tripped and the lights won't come on. Even when we reset the gfci, once we plug in the chord it gets tripped...
View more questions
Search
|