    Heating
    My carrier gas furnace is reading code 13 I had to install a return to a new furnace and keep getting code 13
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #2

    Apr 4, 2016, 02:07 PM
    Sometimes you need to watch the codes carefully. There will be a different time spacing between 13 and 31. The first digit is the number of short flashes, the second digit is the number of long flashes.
    13 is a limit lockout, typically high limit.
    31 is the pressure switch didn't close or reopened.
    13 is usually from air restriction in the return or through the filters, look for dirty filters or collapsed return lines.
    31 can be a blocked flue, dirty orifice on the pressure switch, disconnected hose from the inducer to the switch or a bad switch. I have seen small slits in the inducer line cause the shut down.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Heating and cooling unit blowing air but not heating- goodman [ 1 Answers ]

It is a gas pack. Blowing air but not heating. Could it have a pilot light out?

Carrier heating unit --fan won't work with heating [ 6 Answers ]

I have a carrier heating unit installed in 2000... it worked fine since then but now... fan will work if we turn it ON by itself... but if we turn on auto heat then heater goes on (blower like sound) but fan doesn't force the air into the house... if we turn off the heat... fan comes on...

Cost of converting electric heating to gas heating [ 2 Answers ]

I am buying a house with electric heat. I have heard it can be a lot more expensive than gas. What would be the cost of converting the house to gas heating and a/c?


View more questions Search