    Wet Venting For Vanity & Toilet & Shower
    I want to install a vanity sink and a toilet and a small shower in the east end of my bungalow. The bungalow has a relatively new steel roof, and I so don't want to vent through it. I want to vent through the east wall. My plan is to have all 3 items connect to a new waste water pipe in the joist cavity under the floor, which will connect to the rest of the house plumbing on the west side, to carry the waste water away. Can I use the new waste water pipe that collects the waste from the vanity sink and the toilet and the shower as a wet vent if I extend the waste pipe and turn it up through the east wall plate, up inside the wall, and out the wall at about the 7 foot point, with an appropriate cap?
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #2

    Jan 30, 2016, 02:25 PM
    You need to use the sink vent as the wet vent for the entire bathroom group... not just the drain line. Can you run the sink vent back to the east wall?

    Mark
    fortinlgf's Avatar
    fortinlgf Posts: 5, Reputation: 1
    New Member
     
    #3

    Feb 1, 2016, 05:34 AM
    Quote Originally Posted by massplumber2008 View Post
    You need to use the sink vent as the wet vent for the entire bathroom group... not just the drain line. Can you run the sink vent back to the east wall?

    Mark
    Thanks for the reply. Please look at my rough diagram plan. I was hoping the extended new waste pipe in the joist cavity would provide enough venting for each of the items. 3" waste pipe into 2" vent pipe up through the exterior wall.
    Attached Images
     
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #4

    Feb 6, 2016, 02:28 PM
    The sink MUST BE VENTED... it is this vent that will "wet vent" the other fixtures.
    fortinlgf's Avatar
    fortinlgf Posts: 5, Reputation: 1
    New Member
     
    #5

    Feb 7, 2016, 05:18 AM
    Thanks for the feedback. As I cannot vent through the roof, and it would be very difficult to vent the kitchen sink out the east wall, I would like to use an air admittance valve from Lowe's [Studor brand product # 671806 about $40] Hopefully this could do the work of an external vent.
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #6

    Feb 9, 2016, 05:33 PM
    An AAV is better than no vent. As long as local plumbing code allows, I'd install it at the sink. Take the sink drain directly off the toilet drain and install the AAV under the sink.
    fortinlgf's Avatar
    fortinlgf Posts: 5, Reputation: 1
    New Member
     
    #7

    Feb 10, 2016, 03:09 PM
    Thank you for the feedback - and for giving me the feeling that the real solution is to find a way to have a "real" vent, not just an "AAV". After some careful thinking and planning, I found a way to run a vent from the vanity sink waste pipe, up inside the wall, then along the wall heading east, along (inside) the east wall about a foot where I was able to have the new vent exit through the exterior wall. Looks good. Going to be the best solution.
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #8

    Feb 10, 2016, 04:20 PM
    Yeah, as a licensed plumber, I know there is ALWAYS a way to get a vent run. Good job!

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wet Venting a toilet - IPC [ 2 Answers ]

Hello, I am updating the drains in a home we are remodeling. We are adding a bathroom which will have 1 toilet an 1 double sink on the 2nd floor. In MD and we use IPC I believe. I would like to do the following, is this legit? 3 inch stack leading up from the basement to the toilet...

Wet venting for flush up toilet? [ 3 Answers ]

Can someone explain what wet venting or candy caning is for a flush up toilet system? Or just a simple diagram to where the vent goes?

Wet venting a toilet in the vertical drop? [ 3 Answers ]

I am plumbing a new bathroom in an existing space. The best/easiest place for me to vent the toilet is in it's vertical drop between the joist. From there the drop continues below the joist(less than 24" of drop) before going horizontal to the stack. I have a shower and a sink that will be...

Wet Venting a Toilet? [ 8 Answers ]

Would this be an appropriate way to set up the DWV for this bathroom? I had heard about wet venting from someone else and I want to know if this will work? I think the picture is pretty self explanatory. I plan on plumbing this bathroom with 3" and first hitting the sinks by rolling a reducing wye...

Wet venting a shower and toilet [ 7 Answers ]

I'm in the process of remodeling a bathroom and need help with venting all of the fixtures (toilet/shower/lav). I was thinking on wet venting the shower and toilet from the lav's vent see the sketch below. I was told that this is possible (up to "code") if a 4" drain pipe is used for the water...


View more questions Search