    30A brkr to a 20A brkr
    Removed an electric stove from a double pole 30A brkr and want to replace with a single pole 20A for a new gas cooktop. Must I remove the 10 awg or can I use it with the 20A brkr. I will put a cover inplace to take care of the opening from the double pole brkr I removed.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #2

    Jul 8, 2015, 03:30 PM
    No problem. You can use a 20 amp breaker with 10 gauge wire. Cap both ends of the unused conductor with a wire nut. Probably easier to use two single 20 amp breakers (leaving one for a spare) than to find a blank cover to fit your panel.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #3

    Jul 10, 2015, 05:23 AM
    If It had No Neutral, you can Identify both ends with white tape, also may need to pigtail a short Piece of #12 to attach to the recpticle. If you have a neutral, then you could have 2 20 amp circuits with a 20 amp 2 pole breaker and have each hot go to to separate recpticles, and connect the same neutral to both. Fills the space and gives an extra circuit. Its referred to as a "MultiCircuit"(2 circuits on opposite phases sharing a neutral)On opposite phases, the Neutral carries the DIFFERENCE of the 2 loads, If 1 is drawing 14 amps and the other is drawing 15 amps, the neutral will be carrying 1 amp. Research more or ask anything not sure of if doing a multicircuit. Good luck.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #4

    Jul 10, 2015, 05:37 AM
    Meant to say identify 1 conductor at both ends with white tape. Then place on Neutral bar.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

2 pole 70 amp brkr needed for X-ray unit.limited box.. load test [ 3 Answers ]

Building electrical to sub panel limited. Need 70 amp brkr.. power draw is momentary and infrequent. Is load test needed? If so is this simple or costly? Thank you for any help!:)

My Bryant AC keeps tripping the brkr. It is 4yrs old and has new capacitor and brkr. [ 4 Answers ]

After I reset the breaker my unit will run through a cycle and shut off, when the stat calls for it to start up again the breaker will trip. I had the capacitor replaced last summer and it still looks fine. I replaced the 2-pole 30amp breaker yesterday. It is a bryant model: 661c. Any...

To determine the size amp brkr. For a 5kw a/c unit do I just divide 238 (v.) by 5000 [ 4 Answers ]

To determine the size amp brkr. For a 5kw a/c unit do I just divide 238 (v.) by 5000

Installed recessed lt, addd brkr, light goes low frequently [ 4 Answers ]

Hi We installed recessed light(6), run through new circuit breaker. Now frequently when fridge automatically triggers, all house light dims and come back normal. This happen almost every 5 minutes. Before it newer used to happen. Please suggest what to do

Going from 20A to 30A Breaker with #12 Wire [ 3 Answers ]

Hello everyone, We are having a few issues were our circuit breaker trips when we turn on the microwave. After the circuit breaker tripped we noticed that the power is shared from our small kitchen area to another office and a computer with a desk. The following are the equipments that are...


View more questions Search