    Feb 26, 2005, 06:20 PM
    Venting basement bathroom
    Hi all,
    First time here. I am finishing my basement in Milwaukee. The washer dumps into a sink which has a 2" line that y's into a 4" drain that is stubbed up from the slab. This is not the main stack. The 4" ties to the main 4" about 12' away under the slab.
    The 4" stub rises from the floor about 4' and is then reduced to a 2" which is the drain from the kitchen sink. From the sink it becomes a dry vent which is tied to the main stack vent in the attic.
    I want to put in a toilet, shower and sink. The toilet will Y into the 4" in the horizontal run about 4' from where the pipe turns and comes up. The shower would be the same. The sink would tie into the 4" above the slab.
    From what I have read, the 2" from the sink would be a wet vent for the sink.
    My question is can I vent the toilet and shower into the 2" wet vent from the kitchen? A second option would be to tie them into the dry side of the vent in the kitchen above where the sink ties in? The best option would be that the below grade ties would be vented from the 4 to 2 wet vent and no additional venting would be required. If I am not making sense, I can post a dwg that may clarify. Thanks for any input.
    Scoot
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #2

    Feb 27, 2005, 07:45 AM
    Venting basement bathroom
    Quote Originally Posted by SCOOT
    Hi all,
    First time here. I am finishing my basement in Milwaukee. The washer dumps into a sink which has a 2" line that y's into a 4" drain that is stubbed up from the slab. This is not the main stack. The 4" ties to the main 4" about 12' away under the slab.
    The 4" stub rises from the floor about 4' and is then reduced to a 2" which is the drain from the kitchen sink. From the sink it becomes a dry vent which is tied to the main stack vent in the attic.
    I want to put in a toilet, shower and sink. The toilet will Y into the 4" in the horizontal run about 4' from where the pipe turns and comes up. The shower would be the same. The sink would tie into the 4" above the slab.
    From what I have read, the 2" from the sink would be a wet vent for the sink.
    My question is can I vent the toilet and shower into the 2" wet vent from the kitchen? A second option would be to tie them into the dry side of the vent in the kitchen above where the sink ties in? The best option would be that the below grade ties would be vented from the 4 to 2 wet vent and no additional venting would be required. If I am not making sense, I can post a dwg that may clarify. Thanks for any input.
    Scoot
    Hey Scoot,
    Let me solve your venting questions right now. For openers you can not wet vent a kitchen sink or a bath room lavatory. To do so would be to install a "S" trap and "S" traps are outlawed in every plumbing code going. What you may do, however, is to tie the toilet into the 4" wye and the vented lavatory downstream into the 4' horizontal pipe from the toilet and tie the shower drain back into the lavatory drain so it will be wet vented. The lavatory vent can revent back into the dry side of the kitchen vent at least 6" over the flood rim of the sink. Or if that's not handy consider a spring loaded mechanical vent to vent your bath group. This way your job will be vented legally. Good luck on a major project. Tom
    SCOOT's Avatar
    SCOOT Posts: 3, Reputation: 1
    New Member
     
    #3

    Feb 27, 2005, 01:22 PM
    Thanks Tom,
    I was afraid that was what I would hear. A mechanical vent will be a whole lot easier than tearing up my kitchen. What manufacturer would you recommend for the mech. Vent? Scoot
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #4

    Feb 27, 2005, 02:46 PM
    Mechanical Vent
    Hi Scoot,
    Click on this link.
    http://www.studor.com/homeowners.htm located just north of where I live is the only mechanical vent I would recommend. Pick up your lavatory with a 2" drainage tee and come off the top of the tee with a Studor Vent. Good luck, Tom
    SCOOT's Avatar
    SCOOT Posts: 3, Reputation: 1
    New Member
     
    #5

    Mar 24, 2005, 04:05 PM
    Check out this layout
    Quote Originally Posted by speedball1
    Hi Scoot,
    Click on this link.
    http://www.studor.com/homeowners.htm located just north of where I live is the only mechanical vent I would recommend. Pick up your lavatory with a 2" drainage tee and come off the top of the tee with a Studor Vent. Good luck, Tom
    Hey speedball,
    Can you give me your opinion of this plan. See attached.
    Attached Files
  1. File Type: zip finalplumbing.zip (10.6 KB, 245 views)
  2. speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #6

    Mar 24, 2005, 04:55 PM
    Quote Originally Posted by SCOOT
    Hey speedball,
    Can you give me your opinion of this plan. See attached.
    Checked out your print. Looks good with the possible exception of the basement sink, It would fly here but I don't know your local code. But plumbing wise it would work. Good luck, Tom

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Bathroom in basement venting question [ 1 Answers ]

Hi, I know this has been asked before but I am still a little confused. We are going to instal a bathroom group in a basement. We are too far away from the main line and will need to vent the group but can't access any existing vents. My question is 1. Does the toilet need to be vented in...

Venting a bathroom group [ 2 Answers ]

Venting questions about a second floor bathroom: 1) Can I install a 2" vent behind a WC (the WC is at the end of the line and the vent rises upstream of the WV) and then connect a shower and tub (separate fixtures) downstream from the WC and consider them all vented? 2) Can I drain a pair of...

Basement Bathroom Venting [ 2 Answers ]

I had my rough in inspection yesterday, and everything looked good except my venting for my sinks. I am installing a bathroom lav and a wetbar sink, running into a 2" wet vent that already has a tub/shower on it. Since the distance to the furthest sink is just under 5' from the wet vent I thought...