    Tjmurray's Avatar
    Tjmurray Posts: 1, Reputation: 1
    New Member
     
    #1

    Nov 1, 2014, 10:03 AM
    Weather maker 8000 will not run
    Looked and tested glow coil and is fine. Glows in testing mode. Fans run. Thermostat is sanded and clean. Filter changed. End of my knowledge it runs fan for 60 to 90 seconds and shuts down. Glow coli never glows. In component test it will glow. Any direction anyone can give me? At thermostat it acts like it turns on. Furnace does nothing. When entering into testing mode flashes code 11. Thanks. Code is just all things have been reset. Now solid light no codes blink. Fan turns on but no glow coil lighting up unless in test mode. Referred to codes earlier nothing useful at this point which is more frustrating. But thanks for helping. P
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #2

    Nov 1, 2014, 01:51 PM
    The code index is inside the air handler cover.
    WallyHelps's Avatar
    WallyHelps Posts: 1,018, Reputation: 136
    Ultra Member
     
    #3

    Nov 4, 2014, 06:30 AM
    Does the inducer fan (the little fan in front) run? If so, then you might have an obstruction in the vent pipe. Or it could be a defective pressure switch.

    Theory: When your thermostat calls for heat the draft inducer should start which creates a draft in your vent pipe. If your vent piping is open and your pressure switch is working properly the pressure switch will send a signal to the control board allowing the hot surface ignitor to glow. If the pressure switch does not close, everything shuts down.

    I have TEMPORARILY tested this by shorting across the pressure switch to see if the furnace comes on. However, you MUST figure out why the pressure switch is not closing because if the vent is blocked it is dangerous. DO NOT LEAVE IT THIS WAY.

    Here is a good description of what I'm talking about:
    https://www.arnoldservice.com/proble...board-problem/

    Best of luck. And heed my warning.
    WallyH

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Weather maker 8000 [ 1 Answers ]

My weather maker 8000 won't light the purge works but it won't light there's not even a glow to ignight. The computer board blinks 3 short and 1 long...

Weather maker 8000? [ 0 Answers ]

What is the blower CFM Rating, for the Carrier Weather Maker 8000

Weather Maker 8000 [ 0 Answers ]

I am trying to find a repair manual online for a weathermaker 8000. I need to replace the fan motor. Does anyone know where I might download a manual?

Weather maker 8000 [ 2 Answers ]

If you install a weather maker 8000 upsidedown will it affect anything, or is it happy under any application?

Weather maker 8000 R-W [ 1 Answers ]

We have a weather maker 8000. And we have gotten a code 12 from the L.E.D light. The code means R-W closed. My question is what is the R-W and where is it located on the Weather Maker 8000?:confused:


View more questions Search