    I'm at a loss with ideas except for pulling 10 AWG wire for a huge chandelier
    I'm supposed to pull the wires for a massive chandelier 120 20 watt candle bulbs I come up with 20 amp load by calculation. The guy doesn't want to downsize the bulb wattage to 10 watts as the bulbs are included with the chandelier he also wants it on a 4 way switch as well so is there any way to use anything wire wise less than 10 AWG as 30 amp switches are ugly and expensive I had pulled a 15 amp circuit by itself for the fixture thinking it would be more than adequate well I was wrong when he gave me the bad news I have 2 of these to put up any help would be great.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Sep 30, 2014, 11:49 AM
    I did not back check any of your calculations, but if you need 20 amps, then why not just run a dedicated 20 amp circuit to the fixture and use #12 AWG cable.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #3

    Sep 30, 2014, 12:18 PM
    Pull the 10/2 to fixtures with a 30 amp relay. Use 15 amp circuit to switches to control relay.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    Sep 30, 2014, 12:50 PM
    If this is in a dwelling you cannot have it on a 30A circuit. In other than a dwelling you can put it on a 30A circuit.

    Have you considered feeding the fixture with two 15A circuits? You'll still need a relay though for a 3/4 way switching setup.

    Where is this fixture going?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

What is the ampacity for 8 AWG wire? 50 or 40 [ 12 Answers ]

Every electrician I ask tell me different story This is important since wire are very expensive I am need to connect an air-condition rated 240 50 Amp 3 wires (2 hot and ground) According to the NEC Table 310.16 Allowable Ampacities of Insulated Conductors Rated 0 Through 2000 Volts, 60°C...

#12 AWG copper wire for baseboard heaters [ 18 Answers ]

I want to run a circuit for baseboard heaters and have been told to use #12 AWG copper. I have a total of three heaters in separate rooms each controlled by its own thermostat. I would like to use #14 AWG copper and have calculated the voltage drop with #14 to be less than 1% with all three heaters...

Can I use a single strand of lamp wire as the ground wire for a chandelier? [ 2 Answers ]

I am in the process of rewiring a chandelier to lengthen the chain. I have wired it using a single strand of the insulated lamp wire as the ground - is this safe/ok to do instead of using the exposed copper wiring I typically see for the ground?

AWG wire size [ 1 Answers ]

What is maximum wire size that can be used in 1 1/4" conduit for weatherhead?

AWG requirement for long wire run [ 26 Answers ]

Hi, I'm planning to replace my tank-type water heater with a tankless model. Electrical specs: 60a dp c/b; #6 AWG wire; 11.8kw; 54a max @220v Available voltages: 208v/220v or 240v/277v QUESTION #1: Why the range of voltages for each option rather than just 220v (voltage ...


View more questions Search