    How to check the correct size wire leading to a 100amp subpanel
    I recently had a 100 amp subpanel installed in a basement. The electrician ran aluminum wire from a 100 amp breaker to the subpanel. The subpanel has room for 6 breakers; 4 are installed (20 amp each). I know that aluminum wire carries only 61% of conductivity that same size copper carries. How can I compare the size of the aluminum wire that was installed to a copper wire?
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #2

    Sep 28, 2014, 02:14 PM
    All SER wire is Aluminum now. What does the wire say? Depending on AWG, Aluminum can is only 30% under and that is why the AWG number is lower(more ampacity). The wire should be at least a #1. For long distances, copper wire cost is prohibitive.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #3

    Sep 28, 2014, 02:32 PM
    Brian,
    Did you mean to say 1/0?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    Sep 28, 2014, 02:47 PM
    Quote Originally Posted by Frankdafixer View Post
    I recently had a 100 amp subpanel installed in a basement. The electrician ran aluminum wire from a 100 amp breaker to the subpanel. The subpanel has room for 6 breakers; 4 are installed (20 amp each). I know that aluminum wire carries only 61% of conductivity that same size copper carries. How can I compare the size of the aluminum wire that was installed to a copper wire?
    Why do you need to make this comparison? Do you not trust the electrician who did the installation?

    I will say, in my area #2AL SER is typical. Those who say this is not a legal installation can save it. It's what's done around here, and I agree with it. Simple as that.
    If #2AL is appropriate for a 100A service it's fine for a 100A sub-panel.
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #5

    Sep 29, 2014, 10:19 AM
    Some electrical supply houses sell a gauge which actually matches up to the wire diameter as a reference. But as far as your requirements and depending on the wire covering, #1 is fine for a 100 amp subpanel. Can you read anything at all on the wire?
    Also, there are several charts available which tell you the diameter of any given wire size... you can try that, if you can do it "safely" with the power to the panel turned off.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

100amp wire size [ 1 Answers ]

Hi, I'm running a 100 amp sub panel aproximatly 85 feet from the 200 amp main for an apartment. What size wire should I run?

Adding a second panel to my house 100amp what size wire do I need? [ 1 Answers ]

I am adding a second 100amp circuit panel box for an in-law apartment is 2-2-2 wire the right size since I have a ranch house and the wire will be around 100 feet long and running in the attic which is hot.

Maximum wire size 100amp ge breaker? [ 1 Answers ]

Considering using 1/0-1/0-1/0 aluminum sheathed wire for connection between 200 amp GE box and 100 amp GE box (100 amp breaker to 100 amp breaker)

Subpanel wire size [ 5 Answers ]

I will be adding a subpanel next to the main panel. The subpanel is rated at 100 amp but I want the subpanel to handle a 50 amp pool heat pump along with a few other circuits, ie: 20amp mircrowave, 30 amp dock outlet .and a few spare slots. To make room for the feed , I will have to relocate a 20...

Wire size & conduit size for 60 am subpanel 150 from source [ 9 Answers ]

Indiana question: I want to install a 60amp subpanel 150 feet from the main panel. This is all exposed runs both inside and out in a commercial envirenement. What gauge and type of copper wire and what size conduit whould I use. How often should insert a junction box in the run. John


View more questions Search