    Distance needed for a GFCI outlet in a non-commercial kitchen
    I would like to know the exact distance required for GFCI on a non-commercial kitchen. I thought the minimum requiremnt was 36" between the kitchen sink and an outlet.
    ebaines's Avatar
    ebaines Posts: 12,131, Reputation: 1307
    Expert
     
    #2

    Sep 18, 2014, 06:20 PM
    No. The spacing rule is that every point along the counter top must be within 24 inches of a receptacle. If you have an outlet 36 inches to the left of the sink and 36 inches to the right, you would violate that requirement.
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #3

    Sep 18, 2014, 07:15 PM
    There have been many fairly recent changes in GFCI placement in Kitchens. 24" spacing is correct across a sink line. Along a counter, they can be 48" apart and still meet the 24" rule. In addition, it used to be any distance over 6 ft. from a sink was the GFCI limit. The NEC (NFPA 70 2011 edition) requires GFCI receptacles in ANY area of kitchens of dwelling units where the receptacles are installed to serve the countertop surfaces. It does not mention a distance requirement in kitchens anymore.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Bathroom GFCI's in commercial bathrooms [ 13 Answers ]

I have 4 bathrooms with an outlet next to each sink in a commercial space that will eventually be a production studio. Do I have to run a dedicated 20 Amp circuit to each GFI or can they be daisy chained together?

Changing 15 amp non-GFCI split to 20 Amp GFCI single (kitchen counters) [ 11 Answers ]

I have an older home and I am redoing the kitchen. The kitchen outlets are currently split ones as per the code of the day. They are presumably using 14 gauge wire. (or maybe it may be 12 since it is the 3 wire loomex) It is not practical to re-run the wire. One of them is quite close to a kitchen...

Gfci outlet [ 5 Answers ]

I want to put a gfci outlet in my bathroom where I have to tie into a light on a switch to get the power. There was a outlet previouly but was not gfci (house built in 1960) so I know that the circuit load would be fine. I am fine with the outlet only working with the switch on but is this going...

Outdoor electrical outlet keeps tripping gfci outlet [ 3 Answers ]

Until just recently my christmas decorations would light up when we plugged them into the outdoor electrical outlet. Now when we plug it in the gfci outlet in the garage keeps getting tripped and the lights won't come on. Even when we reset the gfci, once we plug in the chord it gets tripped...


View more questions Search