    Changed bathroom light fixture and now turning on exhaust fan blows the fuse
    Please help! I changed the light and it works fine, but now when it's on and I turn on the exhaust fan, the fuse blows. Everything else on that fuse works fine. What could be going on? I'm baffled by this
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #2

    Jul 20, 2014, 03:14 PM
    You may have misswired the fan. Somehow you have a hot and neutral connected through the switch. It may have been a switch loop but we don't know how it is or was wired. Tell us the wire colors on the fan switch and how they are connected to the fan.
    sm938's Avatar
    sm938 Posts: 3, Reputation: 1
    New Member
     
    #3

    Jul 20, 2014, 05:28 PM
    Thanks for the quick feedback. I didn't change anything on the fan, only changed the bathroom light which is on the same circuit as the fan. The light works fine, as long as the fan is not turned on. I turn the light on, all is good. Turn on the exhaust fan and a little pop noise and the fuse blows and I got to go down to the fuse box to reset the circuit
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #4

    Jul 20, 2014, 05:50 PM
    I can only assume that somehow you misconnected a wire on the light circuit so that the hot connects to ground or neutral , bypassing the motor for the fan. If there are 2 switches, there should be 2 hots, one for the fan and one for the light and a common or separate neutral. Unfortunately, we cannot see the wiring. Obviously it is in the fan side or it would have tripped the breaker (you say fuse but assume breaker or a resettable fuse). Again, how it the switch for the fan wired, 2 blacks or a black and a white-possibly with black tape on it?
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #5

    Jul 21, 2014, 05:37 AM
    Okay, obviously we need some additional information here.

    Are the light and fan two separate devices controlled by two separate switches or is it one unit?

    The previous suggestions are really spot on. If all things in this equation (fan and light) were working properly originally and all you did was swap out the existing light for a new unit, then more than likely neutral and hot were cross connected within the circuit extension feeding the fan.

    Again, because switch loops, note most switches do not use a Neutral connection. They simply interrupt the hot connection and route to the switch and in turn to the device. (white going to the switch is connected to the black hot feed conductor and if that supply feeds another device, there would be two black and one white. The white in this case is "re-tasked" and must be marked with black tape or marker to show that it is being used as a hot conductor.) (black coming from the switch is connected to the light's black)

    The symptom you are describing is that of a neutral short which is indicative of a miss-wired switch unless the fan unit itself is now defective.
    sm938's Avatar
    sm938 Posts: 3, Reputation: 1
    New Member
     
    #6

    Jul 21, 2014, 09:59 PM
    They are controlled by separate switches in a double switch box. Inside it's a sea of wires, with 3 white in a connector, 4 black in a connector and at least 1 white and another larger dark wire with a cloth looking exterior in a third connector. Each switch has 2 blacks connected to it. Could the light still work if reverse-wired? Both wires were black but I was sure I knew which was hot after removing the old light. I assumed it wouldn't work if wired in reverse, so I didn't check that
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #7

    Jul 22, 2014, 06:15 PM
    There is no "reverse" in a switch. You can have power on the top or bottom. You mentioned a white and "dark" wire together. Where do they go? Cloth exterior would indicate a fairly old house. If you have only black on the side by side switches, it would indicate 2 separate power feeds, rather than a shared neutral. You need a test meter to start checking where power comes from and where it goes.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Bathroom Exhaust Fan with light [ 3 Answers ]

Does that mean you have to put a hole in your roof?

Ceiling light changed, now blows a fuse. [ 8 Answers ]

I replace an old ceiling light. When I took out the old one the wire casing was miscolored and brittle and fell apart. The incoming wire is white, black and ground. Then there is an outgoing white, black and ground. I tied in the wires to the light by matching the colors together. The light...

Disabling a bathroom exhaust fan/light [ 1 Answers ]

Our old bathroom exhaust fan/light combo sounds like a jet engine. I would like to disable it until we can get an electrician to replace it. How can I safely do that? There is only 1 switch that controls it and the 2 lights over our sink. We will need the 2 lights over the sink to remain...

Bathroom light/exhaust fan combo? [ 3 Answers ]

By the way, I am no longer appropriately named ineedtosell--I have sold, bought, and now ineedtorepair! I'm in a 1925/6 house in New Jersey with one very tiny bathroom which we are beginning to remodel. (See photo) When we moved in a year ago, an electrician told us that we would not be able to...

Changed from fan to light fixture and now light will not shut off [ 1 Answers ]

Today I tried to replace a ceiling fan to a light fixture. I connected the black to black white to white and copper to ground. I have a red wire that I don't know what goes to. The light now will not turn off. Should the red wire be connected to something?


View more questions Search