    Central A/C problem
    Hi: I'm new to this site and of course I have a problem. I have a Trane 14XLI unit that the AC stopped working on yesterday. The outside unit just hums. The fan is NOT locked up and will engage and run if I push start it. But still no cold air. I suspect the compressor is not kicking on. I realize that push starting the fan is esentially bypassing the capacitor. Now my questions: are the fan and the compressor controlled by the same capacitor? I took the side cover off and can only see I capacitor. Is there a way to temporarily bypass the capacitor to see if the compressor will run? Thanks in advance for any responses.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #2

    Jul 11, 2014, 05:59 AM
    Welcome to the site maraqtop.
    I am not an A/C tech and perhaps I should not respond but I will anyway.

    I have never seen an AC that used the same capacitor for the fan motor and the compressor. The capacitance required for each is vastly different.

    push starting the fan is esentially bypassing the capacitor
    I'll disagree with your way of stating that. Since the fan motor capacitor is a start capacitor, when you spin the fan, you are not by passing capacitor, you are doing its job of aiding the fan motor in getting started. Once the fan motor is up to speed the capacitor is taken out of the circuity.

    Since the compressor motor is enclosed in the "can" there is no way to physically or mechanically do the same for the compressor.

    Trace the wiring from the capacitor to determine if it is for the fan or the compressor. There is usually a big difference in the physical sizes of the two.

    Put your hand on the compressor. You should be able to feel the vibration and heat if it is running.

    The humming you hear is probably the compressor running.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Central heater problem, help! [ 0 Answers ]

I've searched around on the interwebs but can't seem to find any answers to my problem. So it's 100+ degrees here in Missouri and my apartment is a lava pit. I have the AC on full blast and it's doing the best it can but the heat just won't dissipate. I followed the source of heat around my apt and...

Central Air Problem [ 0 Answers ]

My central heat and air unit stopped working properly in the winter months and we had to use the emergcy heat because no matter what temp we set the thermostat to the room would never reach that temp. Now it's around 90 degrees most days and my air conditioning isn't working properly either it...

Central heating problem or water meter problem? [ 3 Answers ]

We live in an apartment building and the individual water usage is measured by private water meters (mechanical). When the apartment was built, 2 years ago, some of the meters had been fitted the wrong way (in reverse). Yesterday a plumber attended to rectify 3 meters. My 2 neighbours meters were...

Central air problem [ 4 Answers ]

When I turn on the central air, it starts and runs fine. I have a programmable thermo. Set at 73 degrees. The problem is this, when it reaches it temp setting it turns off. However when the inside temp rises above the set temp the system turns on, but the part of the a.c. unit that pumps cold...

Central a/c outside condenser problem. [ 1 Answers ]

I have an older Night & Day outside a/c condenser unit. The fan motor stopped running. The fan motor was a replacement, I replaced years ago from a spare unit. All the specs have been washed away by time. I replaced the fan motor with a 1/4 hp, 1625 rpm and new 5 uf capacitor. The new fan...


View more questions Search