    What gauge wire i.e.. (12/2 with ground) will I need to run 50 amp service at 500 ft
    I need to run service to my motor home from the main house 100 amp panel 500 ft away to my motor home which has a 50 amp panel. What gauge is sufficient to achieve this either above ground or direct burial whichever is both cost efficient and safe.
    Studs ad's Avatar
    Studs ad Posts: 134, Reputation: 9
    Junior Member
     
    #2

    Jun 24, 2014, 11:08 PM
    This will give you an idea for 1/0 Aluminum. This calculation is based in part on the amperage actually used. You should provide service for 50 amps regardless of current draw, but the actual voltage drop will vary with the amount of current you use. If you don't use the full 50 amps the voltage drop will be smaller. 2-5% voltage drop is generally accepted. Closer to 2% is better. You could go a larger wire size, but I think you would be fine in this area. This is based on 240 volts at source. If your voltage is lower at the source, then the end voltage will be lower. I've included a link to a calculator to use. Plug in the numbers at 240 volts I am assuming and calculate.

    Voltage Drop Calculator

    Result

    Voltage drop: 7.75 volts
    Voltage drop percentage: 3.23%(larger wire size = smaller drop
    Voltage at the end: 232.25 volts
    Try this link for Calculator.net

    Voltage Drop Calculator
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Jun 25, 2014, 04:22 AM
    As soon as you said 500' you threw cost efficient out the window. That is a loooong way to run line voltage (120/240V).

    IMO 5% is perfectly acceptable depending on the starting voltage. Some places it's nearer to 250V so it can withstand move VD.

    I would also think 1/0AL is an optimal mix of cost and power efficient.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Do we need another transformer for 500 foot run and what gauge wire? [ 5 Answers ]

We are adding a shed and will be running a new line from the electrical pole. The shed will be approximately 500 feet from the pole. Prior to the pole, this will also branch off to go to a new above ground pool to power the pump. Our question is if we can just run the line straight to the panel...

Wire service, wire gauge 100 amp [ 9 Answers ]

I'm installing a 100 amp service in the backyard with a separate meter on a pole next to sub-suface power tranasformer. I have a 100 amp meter box on one side of the pole and a 100 amp braker panel with a 100 amp main breaker on the other side. I'm going to place in it a 15-20 amp breaker for gfi...

I need to run 220 amp service to an airconditioner will 6 gauge wire handle 40 amps? [ 4 Answers ]

I need to run 220 amp service to an airconditioner will 6 gauge wire handle 40 amps?

What gauge wire is needed for a 600' run to my dock so I can have 30A service? [ 1 Answers ]

I have a long run to my dock so need to know the gauge of wire needed to run so that I have have a 30A panel on the dock.

What wire gauge for 400 amp service, 320 ft run? [ 7 Answers ]

Built a pole barn in the back yard, was going to upgrade the house service and run from there, but thanks to the county I am running separate service. I have the 3" conduit, I know I need to leave 35' coiled at the bottom of the utility pole, and want to run about 5' inside the barn to get to...


View more questions Search