    Chilled water expansion vessel
    How do I size a chilled water expansion vessel for a closed circuit system?
    schildermans's Avatar
    schildermans Posts: 3, Reputation: 2
    New Member
     
    #2

    May 8, 2007, 12:02 PM
    The expansion vessel should prevent the built-up of high pressure in case the chiller stops and the water takes the temperature of the surrounding air.You have to calculate the water mass entrapped in the system,and multiply this by the difference in specific volume.
    E.g the specific volume of water @ 0°C is 1.000 liter/kg, at 50°C it is 1.012 liter/kg.
    koolhead45's Avatar
    koolhead45 Posts: 1, Reputation: 1
    New Member
     
    #3

    May 27, 2007, 11:02 AM
    Differents parts of HVAC Chilled Water System

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Chilled water pressurization unit [ 3 Answers ]

1- what is the function of the pressurization unit in chilled water system and can the system operate with out it i.e with expansion tank only 2-what the correct arrangement of pressurization unit+expansion tank+air separator.. I mean how these are linked together

Chilled water pump for HVAC [ 15 Answers ]

Kindly let me know what pump I should use for a chilled water close loop system where required flow rate is 102 m3/hr and the max. hight of building is 100 ft.

Chilled water pipe [ 3 Answers ]

I am very new to askmehelpdesk.com. My question is, The building height is 300m. There are 6 chilled water risers going up to 125m height. The chilled water flow rate of each riser as follows. Riser 1 & 2 - 150l/s Riser 3 & 4 - 180l/s Riser 5 & 6 - 100l/s Chilled...


View more questions Search