    Thermostats
    We live in an old 2 storey house.Thermostat is in the hall on the second floor. We have just installed a new gas furnace and now the temparature on the second floor is about 5-10 degrees warmer than the first floor. Should we move the thermostat to the first floor?
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #2

    Feb 25, 2014, 05:34 PM
    Hmmm...

    If I follow you here, you are asking if you should move the thermostat to the colder area (1st floor) because the 2nd floor is 5-10 degrees warmer, right? By my thinking that would just end up resulting in an even warmer 2nd floor, right? Here, by comparison to the 2nd floor, the colder 1st floor would only serve to have the furnace stay on longer to satisfy the thermostat...just make the 2nd floor even hotter as the 1st floor got comfortable!

    I'm thinking that you may want to check the air vents/registers in each room and see if they are adjustable. If the registers are adjustable I would start by opening the ones on the 1st floor wider and closing the ones on the 2nd floor a little bit....see if that makes a difference. Using this approach and purchasing a cheap battery powered room thermometer you should be able to figure a decent balance between floors. If you don't have adjustable registers then you may want to look into purchasing some (available in multiple sizes). There are other answers, too, but this is the easiest place to start.

    In some cases, you might need to install dampers (flow control) in main trunk lines. In rare cases, we'll even install fans to "boost" air flow to certain rooms or floors.

    Anyway, let me know what you think, OK?

    Mark

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Need help replacing master and slave thermostats to z wave programmable thermostats [ 0 Answers ]

Hi all! Im looking to replace my old thermostats with z wave programmable thermostats. I have a 3 zoned heat/ac system that has one master thermostat with wires R Y W G B O and two slaves with just R Y W. The trouble is finding a thermostat with separate B and O connections. Must installation...

Noma thermostats. Has there been a recall for any of these thermostats [ 1 Answers ]

Has there been a recall for any Noma Thermostats. Recently my neighbor had a fire in his basenment and the fire department said it was electrical, caused by the thermostat and they told him there had been a recall on these thermostats

Thermostats [ 0 Answers ]

How to upgrade my trane baystat 239 with a luxpro psmh45 were would my wires go

Can Honewell Thermostats be used to replace Intertherm Thermostats? [ 1 Answers ]

A quilt rack fell on the Intertherm and damaged it. Now, it acts like it's not getting power. The fan won't even blow. We've replaced with a Honeywell, only to have the same problem.

Thermostats [ 1 Answers ]

Hope there is someone that can help me out my mother lives about an hour and a half from me and I was hooking up a thermostat for her heating and cooling unit her old unit was a rheem and the new one was a honeywell and the wiring digram was totally different is there anyone out there that can tell...


View more questions Search