    No heat on First Floor
    We have hot water baseboard, 1 circulator, 2 zone valves, 2 thermostats (1st flr, 2nd flr), Honeywell. Last week 1st flr heat stopped working. Forecasted to be cold in a couple of days, need to fix this. I think it's the powerhead on the 1st floor zone valve but need to make sure before I buy one.

    With the furnace warm, if I manually open the 1st flr zone valve we get heat to the 1st flr.

    If the furnace is cold and the 2nd flr stat is NOT calling for heat, if I turn the 1st flr stat all the way up the furnace DOES NOT come on. I thought this might point to a bad stat but if I cross the 1st flr stat wires the furnace still does not come on.

    Thanks for any Help
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Apr 2, 2007, 06:06 AM
    If you turn on the first floor T-stat does the pump run?


    ((With the furnace warm, if I manually open the 1st flr zone valve we get heat to the 1st flr.))

    If you open the first floor valvae manually does the heat come on when boiler cold?
    KKfromNJ's Avatar
    KKfromNJ Posts: 6, Reputation: 1
    New Member
     
    #3

    Apr 2, 2007, 07:00 AM
    Thanks for your help.

    The only time the furnace fires and/or the pump comes on is when the 2nd floor stat is calling for heat
    KKfromNJ's Avatar
    KKfromNJ Posts: 6, Reputation: 1
    New Member
     
    #4

    Apr 2, 2007, 07:03 AM
    Funny thing (to me) is when I was checking the 1st flr stat, turning all the way on and off, I expected to see the little spark in the merc capsule but didn't. When I shorted the 1st flr stat wires I saw no spark.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #5

    Apr 2, 2007, 08:35 AM
    It could be the power supply for the first floor area. Transformer I suspect. Get out the volt meter and start back tracking to find the problem.
    KKfromNJ's Avatar
    KKfromNJ Posts: 6, Reputation: 1
    New Member
     
    #6

    Apr 2, 2007, 08:59 AM
    There is only 1 transformer
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #7

    Apr 2, 2007, 09:05 AM
    You still need to trace back to find what happened to the signal from the first floor.
    KKfromNJ's Avatar
    KKfromNJ Posts: 6, Reputation: 1
    New Member
     
    #8

    Apr 3, 2007, 10:44 AM
    I changed the power head, all is GOOD! Thanks to everyone for their comments.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Tile leak from 3rd floor through 2nd floor ceiling (bath) [ 5 Answers ]

Hi All: We renovated our third floor bathroom which included stripping the floor down and installing tiles (1" squares within 1' blocks). After our 3rd floor tenant takes long showers we get some leakage through her floor and thusly through our ceiling (which we now have partially open to have...

1st floor ceiling leak below 2nd floor shower [ 2 Answers ]

Our ceiling has developed a swelling or bubble in the ceiling and when touched-it literally fell apart and created a hole. It is dry to the touch but happens to be right in line with our 2nd floor master bedroom shower where the plumbing probably comes down. The shower has a plastic floor with a...

Proper underlayment for vinyl floor starting at floor joists [ 2 Answers ]

What is the proper way to build up a floor to prepare for vinyl flooring? I'm building a mud-room in the garage attached to the house, 5' by 13' . Presently I have the joists installed and am ready for subfloor. I am planning to use 3/4" T&G UDL plywood, glued to joists with construction...

Trouble getting heat to 2nd floor [ 3 Answers ]

I live in a two floor home where the thermostat is on the first. The trouble is I am having trouble getting heat to the 2nd floor. Is there any thing I can do to the vents on the 2nd floor that would allow heat to reach up there?

Nuheat Electric Floor Heat [ 2 Answers ]

Hello, I am installing a Nuheat (Nuheat.com) electric floor heating pad. There are 2 wires from the pad that need to run up the wall and into a switch box. The switch box will have power coming in which connects to the thermostat and the thermostat connects to the heating pad. Does the wires...


View more questions Search