    WeatherMaker 8000 -- HSI Never Glows
    My WeatherMaker 8000 seems to not be heating up properly. When I switch on power to it and let it fire up, the inducer switches on and it seems like air is flowing. But I never see the HSI glow or the burners switch on.
    When I examine the status light, it appears that it is showing a code of 31. Three short lights followed by one long. I've attached a video of the start up here:

    https://www.dropbox.com/s/9hpezouv5hcy5oh/IMG_1714.MOV

    I'm not very familiar with HVACs, but I'm wondering what steps I can take to diagnose this issue? Is it something I can fix myself or do I need a professional?
    WallyHelps's Avatar
    WallyHelps Posts: 1,018, Reputation: 136
    Ultra Member
     
    #2

    Feb 3, 2014, 05:46 AM
    The HSI is one of the easiest parts to replace in this furnace. Take it out (carefully, as it is ceramic and fragile) and check the resistance between the two contacts. I'm not sure of the "good" value, but if the resistance is infinite, the HSI is burned out. You may or may not be able to see a small crack in the black ceramic.

    Go to a good appliance parts store and get an equivalent HSI. Should be $25 or so. Put it in and enjoy the heat!

    Good luck,
    WallyH
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #3

    Feb 3, 2014, 02:58 PM
    Just because the HSI doesn't light doesn't mean it is bad. Could be a non reset safety switch, could be a high temp overload. Don't just replace parts . Read the blink code, usually on the inside of the air handler door or on the control board. If it is a HSI, most are very easy to replace, $25-40
    WallyHelps's Avatar
    WallyHelps Posts: 1,018, Reputation: 136
    Ultra Member
     
    #4

    Feb 4, 2014, 05:13 AM
    Very true! You hope it is the HSI, as it is inexpensive and simple to replace. However, test it as I indicated before buying a new one. Since you are getting an error code, you should focus on that area. As ma0641 says, it could be a switch, etc. causing the problem.

    Good luck,
    WallyH
    Grady White's Avatar
    Grady White Posts: 1,417, Reputation: 59
    Ultra Member
     
    #5

    Feb 4, 2014, 08:56 PM
    Before replacing parts, TEST. If you have a voltmeter & know how to use it, during the whole ignition process check for 120 volts to the ignitor. If you get 120 volts & the ignitor does not glow, replace the ignitor. If you do not get the 120, most likely the problem is a venting issue.
    easyas1234's Avatar
    easyas1234 Posts: 7, Reputation: 1
    New Member
     
    #6

    Feb 4, 2014, 08:57 PM
    Measure my old HSI. Resistance was infinite. SO I bought a brand new one and installed it just as the instructions suggested. Still though when I switch on the heater, I don't see it glow.The inducer comes, I can hear air blowing. However if I look around the house I don't feel any air out of the vents. Nor do I see anything happening with the burners.What should I check next? I've never fixed one of these before. So I'm not sure what I'm looking for always. And the manual I found for my unit does not match up very well to the actual control board that I'm working with at the moment.Thanks.
    parttime's Avatar
    parttime Posts: 1,440, Reputation: 113
    Ultra Member
     
    #7

    Feb 5, 2014, 03:32 AM
    Hi easy, do you have the 120 volts at the ignitor? Did you have 120 volts at the old one?
    WallyHelps's Avatar
    WallyHelps Posts: 1,018, Reputation: 136
    Ultra Member
     
    #8

    Feb 5, 2014, 06:51 AM
    Diagnostic Procedure
    You may want to run the built-in self-test. The procedure below may not match exactly your board, but it should be close. I agree with the other posters that you should check for 120 volts at the HSI connector, and you can do that by disconnecting the HSI and plugging your meter into the plug during the test. When you get to the step that powers the ignitor, you should see the meter jump to 120 volts.

    Component test—The furnace control board allows all components, except gas valve, to be run for a short period.
    This feature helps diagnose a system problem in case of a component failure. To initiate component test procedure, short
    (jumper) the TEST 3/16-in. quick connect terminal on control (behind the Y/Y2 terminal) and the COM-24V terminal on
    furnace thermostat connection block for approximately 2 sec.

    NOTE: Component test feature will not operate if any thermostat signal is present at control board.
    I disconnect the thermostat wire from the R terminal right there on the main board.

    Component test sequence is as follows.
    a. Momentarily jumper TEST and COM-24V terminals until LED goes off.
    b. LED will display previous status code 4 times.
    c. Inducer motor starts and continues to run for entire component test.
    d. Hot surface igniter is energized for 15 sec, then deenergized.
    e. Blower motor operates on FAN speed for 10 sec, then stops.
    f. Blower motor operates on HEAT speed for 10 sec, then stops.
    g. Blower motor operates on COOL speed for 10 sec, then stops
    h. Inducer motor stops

    Don't forget to hook the thermostat wire back up!
    Name:  furnaceboard.jpg
Views: 2272
Size:  56.6 KB

    WallyH

    P.S. You had mentioned earlier that you had a code 31. For my furnace, that indicates these possible problems (note HSI is not in here!):

    PRESSURE, DRAFT SAFEGUARD, AUX-LIMIT SWITCH (when used*) OR BLOCKED VENT SWITCH (when used) DID NOT CLOSE OR REOPENED
    (DOWNFLOW ONLY*) If open longer than five minutes, inducer shuts off for 15 minutes before retry.
    Check for: - Proper vent sizing
    - Low inducer voltage (115VAC) - Defective inducer motor
    - Defective Blower motor or capacitor - Restricted vent
    - Defective pressure switch - Excessive wind
    - Inadequate combustion air supply
    - Disconnected or obstructed pressure tubing
    If it opens after trial for ignition period, blower will come on for 90 second recycle delay.
    easyas1234's Avatar
    easyas1234 Posts: 7, Reputation: 1
    New Member
     
    #9

    Feb 6, 2014, 05:50 PM
    All right everyone. Thanks so much for the comments. Here is my progress so far:

    1) I've confirmed that I am getting 120V at the ignitor
    2) I ran the self test. The self test seemed to run all tests successfully. The inducer came on, the HSI lit up, and the 3 blower tests occurred. I've added a video just in case I missed something:

    https://www.dropbox.com/s/vi88lmjlvi..._self_test.MOV

    So in terms of code 31. I think that the below possibilities are not the problem:

    - Low inducer voltage (115VAC) - Defective inducer motor
    - Defective Blower motor or capacitor - Restricted vent
    - Inadequate combustion air supply

    What it seems like it could be is one of these:
    - Defective pressure switch - Excessive wind
    - Disconnected or obstructed pressure tubing

    I figured that I should check my gas vent and see if it is obstructed. My gas vent goes from my condo up into the roof of the building. I went an check it and found this:

    https://www.dropbox.com/s/20wjts92pebyece/hvac_vent.JPG

    It looks like my vent cover is gone! So I turned my HVAC back on and stood up there to see if any gas was coming out. Sure enough there was gas coming out. I know I need to fix this and cover that, but I don't think its getting blocked.

    What steps should I take now? Could it be the pressure switch? What other things should I test? Thanks so much for all the help.
    WallyHelps's Avatar
    WallyHelps Posts: 1,018, Reputation: 136
    Ultra Member
     
    #10

    Feb 7, 2014, 07:04 AM
    First off, well done on your diagnostics work! You are rapidly reaching the limit of my ability to offer additional help. Hopefully some of the experts in this area can chime in.

    I think testing the pressure switch is a great next step. You need to know if it is the switch itself, or if the switch is indicating an actual safety problem.
    Grayfurnaceman on YouTube has a good video that might help you here. If you're like 99.999% of the population, you won't have a manometer (neither do I), but if it were me, I would pull the tube from the switch and see with your finger if there is any vacuum when you are running the self-test. It's not exact, but might be a quick go/no-go indication.

    Best of luck,
    WallyH
    Grady White's Avatar
    Grady White Posts: 1,417, Reputation: 59
    Ultra Member
     
    #11

    Feb 7, 2014, 03:32 PM
    Easy,
    Once you check the switch with the ohmmeter as shown in the video, if you find the switch is not closing & the pressure spec is on the switch, you can get an approximate idea of what the venter is doing by using the homemade manometer shown here:
    RV U Tube Manometer
    You will need a barbed adaptor to adaptor to go from the size of your tubing to the 1/2" used on the manometer. You can use tubing smaller than the 1/2" if you so desire.
    easyas1234's Avatar
    easyas1234 Posts: 7, Reputation: 1
    New Member
     
    #12

    Feb 7, 2014, 11:47 PM
    Ugh, I figured it out. There is a button on the pressure switch. When I pressed it everything started working. I don't remember seeing anything about that in the manual. But it was very easy to fix :-\. Thanks for all the help though, I certainly learned a lot with this exercise.
    parttime's Avatar
    parttime Posts: 1,440, Reputation: 113
    Ultra Member
     
    #13

    Feb 8, 2014, 01:01 AM
    Thanks for the update, this will help someone later I'm sure.
    Grady White's Avatar
    Grady White Posts: 1,417, Reputation: 59
    Ultra Member
     
    #14

    Feb 8, 2014, 02:06 PM
    I don't recall as to ever having seen any kind of button on a pressure switch. Can/would you post a photo of it?
    easyas1234's Avatar
    easyas1234 Posts: 7, Reputation: 1
    New Member
     
    #15

    Feb 10, 2014, 10:16 AM
    Okay. Here is the picture. You can see between the two orange leads a little tab there. By simply pushing that knob I was able to fix the problem.

    Attachment 45648
    Grady White's Avatar
    Grady White Posts: 1,417, Reputation: 59
    Ultra Member
     
    #16

    Feb 10, 2014, 06:24 PM
    Sorry easy, I couldn't see the attachment.
    easyas1234's Avatar
    easyas1234 Posts: 7, Reputation: 1
    New Member
     
    #17

    Feb 14, 2014, 05:06 PM
    Let me try with dropbox. Can you see this link:

    https://www.dropbox.com/s/x549pu6e33...SwitchKnob.jpg
    Grady White's Avatar
    Grady White Posts: 1,417, Reputation: 59
    Ultra Member
     
    #18

    Feb 14, 2014, 05:08 PM
    That's not a pressure switch. It is a thermal limit & will trip if it gets too hot. The pressure switch is the device below the limit.
    parttime's Avatar
    parttime Posts: 1,440, Reputation: 113
    Ultra Member
     
    #19

    Feb 14, 2014, 05:21 PM
    Hi easy, that looks more like a limit switch to me, does it have a tube running to it?

    sorry Grady, I type slow.
    easyas1234's Avatar
    easyas1234 Posts: 7, Reputation: 1
    New Member
     
    #20

    Feb 16, 2014, 12:05 PM
    Ah yeah, knew I said the wrong thing. It's the limit switch. Easy fix :-\.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

What is wrong with my WeatherMaker 8000? [ 0 Answers ]

This gas heater has been working for the last 15 years no problems. I turned the thermastat to warm up the place and I only get air no heat. I checked the fuses and they are all good, I crawled up the attic and unable to find where the Pilot light is located. The gas is on and I didn't smell...

Weathermaker 8000 [ 0 Answers ]

Weathermaker 8000 failure #34 goes to #14 I reset it by removing the panel and replacing it then it runs fine till the next time it wants to start up what s up with that I've removed the res panel in the lower section middle area with the two red wires going to it and on the back side is two rods...

Carrier Weathermaker 8000 igniter never glows [ 1 Answers ]

I have a Carrier weathermaker 8000 Product # 58ZAV050--16112 Series 160, Model 58ZaV050-12, Series 0802A72264. The unit is not working, i.e. getting hot air and I get error code 34 then after 3 tries(as it should according to manual) I get error code 14. I powered off the unit to begin...

Weathermaker 8000 keeps running [ 1 Answers ]

I have a weathermaker 8000 furnace and the fan motor runs constantly even when the heating cycle is done. I do not have a/c installed and I cannot locate a fan only switch. Is this normal for this unit?

Code 31 on weathermaker 8000 [ 3 Answers ]

I have a weathermaker 8000 58wav. It will startup, induction fan on, flames on, blower on for about 80 seconds. It then shuts down the flame and the induction motor. The blower will run for a short time and off. Blinks 31. Pressure switch was Ok, Flame sensor seems Ok. I checked the chimney vent...


View more questions Search