    I need to run power from a main panel to a shed 175 away.
    I need 3 circuits in the shed. One 20 amp and two 15 amps. Should I run 30 amps of 220 into a sub panel and split there or 2 runs of 30 amp 110?
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #2

    Jan 26, 2014, 04:45 PM
    110 and 220 do not exist anymore, it is 120 and 240. I would run a piece of #8/4, because of the distance, and a small subpanel. Subpanel install requirements have changed over the past few years, be sure to read up on them. You will need a grounding rod at the shed.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Jan 26, 2014, 06:16 PM
    What are the circuits for?
    If you really need three 120V circuits then a sub-panel is your only choice.
    If you can get away with two 20A circuits then you can run one multi-wire circuit which is two circuits sharing a neutral. This is also an easier choice because no ground rods are necessary then either.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

I have a 125 amp. Main panel.no space can I run small sub panel [ 2 Answers ]

I have a 125 amp. Bryant main panel that is maxed out with piggy back breakers. Can I feed a small amp. Panel off the main if I remove some breakers and put them into the sub panel , I need to run a 2 pole 30 amp. On the sub panel.

Do I run a ground from my main panel to sub panel [ 9 Answers ]

I am installing a 100 amp sub panel next to the main panel at our office. There is an existing 100 amp sub panel by the main 400 amp panel and who ever did the work did not run a ground wire from the main to the sub panel. There are mant green ground wires landed on the ground bar but I'm thinking...

How to run power from main panel to garage [ 1 Answers ]

I recently build a second separate garage. I have done the interior wiring and was going to upgrade the house service to 400 amps (from 200 amp) and run 200 amps to the garage. The main reason is that the power company did not want to run directly to garage due to 1. having to go around septic...


View more questions Search