    No heat
    Model No. TBUG-BR045A1NS111 Is not igniting the gas to throw heat out of the unit. I do not measure 24V at the red and white wire of the thermostat or at the back of the heating unit itself. I shorted the red and white wires together from the thermostat and still unable to have the igniter kick in. What would be my next options?
    jbstrieri's Avatar
    jbstrieri Posts: 2, Reputation: 1
    New Member
     
    #2

    Jan 5, 2014, 12:26 PM
    No heat
    Forgot to mention this is a Beacon Morris 45000BTU Garage Heater about 6yrs old Model No. TBUG-BR045A1NS111
    Grady White's Avatar
    Grady White Posts: 1,417, Reputation: 59
    Ultra Member
     
    #3

    Jan 5, 2014, 03:37 PM
    Is there power going to the furnace? If so, find the transformer & check for 24 volts AC there. If there is none, check the incoming side for 120 volts AC. If there is power in but none out, the transformer has gone bad.

    Afterthought: Make sure any doors are in place thus depressing any switches which need to be depressed to allow current flow.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Heat pump never turns on, handler blows continuous with no heat except with AUX heat [ 2 Answers ]

10 year old Rheem air handler RHBA-21J8MFCA, 1/3HP, 2.8A. New WeSt Columbia, SC 29170, Model 2HP13L48P-1B, HCFC-22, 4TON. Installed new out of box iN July and AC working splendidly but start-up is "violent" and loud. Installer says I need some sort of "start-up kit". I put off as had planned...

Kenmore dryer won't heat.changed the heat element+thermal fuse.still won't heat [ 1 Answers ]

Kenmore dryer(110.96582100) is 15 years old. Worked great until it stopped heating. Actually it started taking longer and longer to dry the clothes. But now it won't heat at all. I've changed the heating element and thermal fuse. Could it be the thermistor or high limit thermostat? Don't want...

Heat Pump blows 5amp fuse when switching between defrost & back to heat. Them Heat work [ 3 Answers ]

I have a Carrier Heat Pump System. It’s about 5 years old and has functioned OK until this Christmas Eve. One problem is the condensing unit is not kicking back on after it goes into defrost mode. I found a 5AMP fuse blown in the attic unit and once replaced it functioned. At least for a day or two...

My heat pump is not blowing out enough heat to heat the house [ 0 Answers ]

My heat pump is not blowing out enough heat to warm some room in the house, but the two rooms that close to the heat pump get nice and warm.


View more questions Search