    My water preasure is 140psi adjusted the regulator did not change
    My water preasure is 140psi I tried to adjust the regulator but it did not change. Does this mean the regulator is bad.
    The reason I ask is I just replaced my the hot water tank the pressure relief valve leaks water after there has been a high demand. The hot water tank has a expansion tank I did check the filling valve to make sure there was no water coming out of it when I press on it to release air it is OK
    parttime's Avatar
    parttime Posts: 1,440, Reputation: 113
    Ultra Member
     
    #2

    Dec 31, 2013, 04:21 AM
    Hi deacon and welcome, did you make the adjustments with the water turned off? With about a half turn at a time then re-test?
    Are you saying you changed your water heater because the pressure relief valve was dripping?
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #3

    Dec 31, 2013, 05:13 AM
    If your water pressure is 140 pounds and you cannot adjust it with the PRV, the PRV is defective. Replace.
    Milo Dolezal's Avatar
    Milo Dolezal Posts: 7,192, Reputation: 523
    Plumbing Expert
     
    #4

    Jan 3, 2014, 10:17 AM
    I would do the following:

    1. Make sure PR is not defective (measure Before and After PR. Reading should give you two different values)
    2. Make sure PR is installed with Flow Arrow pointing in the right direction (Arrow marked on body of PR pointing towards the house)
    3. Make sure PR is installed on house plumbing system, not on irrigation branch
    4. Make sure there is no non-pressure regulated water looped back into the house (like connecting sprinkler pipe in the back into the house plumbing system )

    Also, take a water gauge and go around the house measuring pressure at different outlets. Find out which one has reduced pressure and which ones don't.

    Last but not the least, read the label on your PR and make sure it says "15-75 psi".

    Back to you

    Milo

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Replaced the water heater but there is no hot water preasure upstairs [ 8 Answers ]

Replaced the water heater and there is no hot water coming out upsatirs. Downstairs there is hot water coming out but low preasure

Low water preasure in kitchen [ 1 Answers ]

We replaced the water line in kitchen. It was leaking; Now there is far more less preasure. The water preasure is so low I cannot use the sprayer

Hot water preasure [ 3 Answers ]

I have recentley change the ball cock on my hot water tank and in doing some small peaces of chipboard went into the tank and into the pipes now the water flow is very low how can I resolve this

Low water preasure [ 1 Answers ]

I have two bathroom side by side on my second floor. One shower has good water preasure but the other trickles out. Can this be fixed? Thanks, Rob

Water preasure [ 2 Answers ]

What's the relation between the head of water column in atank and its pressure?


View more questions Search