    roadcrossmtb's Avatar
    roadcrossmtb Posts: 4, Reputation: 1
    New Member
     
    #1

    Dec 5, 2013, 02:44 PM
    Furnace blower cycles on/off
    Have a 2004/5 Comfortmaker furnace/air unit. Blower cycles on and off while furnace is fired up. Also cycles when furnace is turned off and fan on thermostat is turned to "On" (as opposed to "Auto"). No fault codes are flashing on the control unit. Some condensation on the exhaust piping. Problem has cropped up in the midst of recent cold snap. Filter is clear. Vacuum tubes in unit are clear. Thoughts?
    roadcrossmtb's Avatar
    roadcrossmtb Posts: 4, Reputation: 1
    New Member
     
    #2

    Dec 5, 2013, 02:45 PM
    ... again, the furnace/flame works fine and stays on. It's only the blower. Thanks!
    Grady White's Avatar
    Grady White Posts: 1,417, Reputation: 59
    Ultra Member
     
    #3

    Dec 5, 2013, 08:58 PM
    You need to check for 120 volts between the fan motor terminal on the control board & neutral or gound while the blower is acting up. If you are losing power, I'd say it's a bad board. If 120 volts is consistent, it's likely a motor problem.
    roadcrossmtb's Avatar
    roadcrossmtb Posts: 4, Reputation: 1
    New Member
     
    #4

    Dec 12, 2013, 09:21 AM
    Thanks Grady! Replaced motherboard. Worked all day yesterday. Woke up to same issue. Thoughts?
    Grady White's Avatar
    Grady White Posts: 1,417, Reputation: 59
    Ultra Member
     
    #5

    Dec 12, 2013, 08:57 PM
    I doubt there is any kind of low temperature contol for the fan. I'm sure it's all timed. With the fan motor cycling on & off, check the motor to see if it is hot. If so, it could be the motor or as simple & inexpensive as a capacitor.
    roadcrossmtb's Avatar
    roadcrossmtb Posts: 4, Reputation: 1
    New Member
     
    #6

    Dec 12, 2013, 09:40 PM
    Motor tests OK. On this model, there is a separate control unit for the blower. It appears be functioning improperly. There are several large capacitors in it. Unfortunately, comfortmaker no longer makes the control unit separately. It is only sold w the blower ($1200) AND is not avail until Jan 16. Not sure I am qualified to mess w the caps in the unit...
    Grady White's Avatar
    Grady White Posts: 1,417, Reputation: 59
    Ultra Member
     
    #7

    Dec 13, 2013, 05:50 PM
    Never seen such. Can you take & post a photo?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

My blower fan/furnace motor on my natural gas/air conditioning system short cycles? [ 1 Answers ]

This summer I had my air conditioning unit replaced after the previous one unknowingly froze up and as a result blew up. The new unit was working well after it was installed in conjunction with the natural gas furnace without issue - albeit the blower on the furnace unit distributes the cold air...

A/C blower cycles on and off? [ 2 Answers ]

Hello, I have a Rheem central A/C that cycles on and off too often. I can hear the compressor run, shut off, and immediately crank up again. Then it shuts off and on again, etc, etc. I am worried about too many restarts being bad for the motors. I connected a digital thermostat some years ago...

Ac blower cycles on/off at start [ 4 Answers ]

When the outside temp closes in on the thermostat set temp ( at night ) the ac will cycle on but the blower will try to start then turn off. It cycles like this for a number of times before finally overcoming the issue and then it will run normally. If during this cycling I move the thermostat to...

Heatpump blower cycles on off [ 1 Answers ]

The heatpump works but the blower has problems. When the fan is put to "On", or when the system is initiated by the thermostat, the blower sometimes will try to start, but cycles on/off. I can hear the relay clicking. When the system does operate correctly the problem will eventually re-occur....

Furnace blower cycles with Thermostat off [ 2 Answers ]

Have Goodman Furnace built 1994. Worked fine until about 3 weeks ago. It starts cycling, and the heat icon does not show on the thermostat. I turn the thermostat off, the furnace continues to blow. Last night to verify, took the thermostat off the wall (but still had the furnace plugged in and...


View more questions Search