    Microwave continues to trip breaker and it's on a dedicated 20amp circuit.
    I've used two different microwaves and both do the same thing, but it only does this at the initial start up. I checked the amperage while the microwave was running, and it's only drawing 10.8 amps. I even plugged a hair dryer in the same receptacle as the microwave and ran both loads for 5 minutes and it did not trip the breaker and it was drawing 19.7 amps.but once again after a few starts of the microwave it tripped the breaker. I have no clue what the issue could be and again this is two different microwaves.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #2

    Dec 4, 2013, 07:50 AM
    Check for loose connections on the breaker, and check the buss the breaker plugs onto. Could be a bad breaker, swap with another 20 amp breaker, and see how it does.
    drtom4444's Avatar
    drtom4444 Posts: 3,282, Reputation: 145
    Ultra Member
     
    #3

    Dec 6, 2013, 11:07 AM
    A microwave must have an initial high load or, as suggested above, you have loose connections in your breaker box. I would not just check the breaker that is tripping, but all of them. The ones on either side could be getting hot and causing the one that is tripping to be more sensitive. When one is loose it's a good bet that all of them need tightening. They get loose over time, and this applies to all wiring connections, including the ones in your receptacles which will cause a fire fairly easily without ever tripping a breaker until the fire is burning. I had wires in my house burn the insulation eight inches or more from the receptacle and destroy the receptacle from loose connections. It happened in several switches and other receptacles, too. Go around your house and check all of the connections. It's very good fire prevention, too. You should check this out: Powerbox | Powering Progress | Power Solutions For Solid State Lighting | Inrush Current

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Dedicated microwave outlet blown, no tripped circuit breaker [ 7 Answers ]

I have an over-the-range microwave with a dedicated outlet. Using it today, heard loud buzz and pop. On investigating, found microwave with no power, and unused plug of outlet had one hole with apparent burn mark. Circuit breaker did not trip. Turned off breaker, unplugged microwave, and...

Arc fault breaker continues to trip [ 2 Answers ]

I recently installed some canned lights and an arc fault breaker. When I hooked everything up, put a light bulb in one of the lights and then turned on the breaker the breaker popped. There is a 3 way switch--7 recessed lights and another 3 way switch with the power coming in to the first 3 way. If...

I plug in a new microwave 120 vac, turn it on high it trip the breaker, why [ 1 Answers ]

I plug a new microwave, turn it on high power, it ran for a few minute that it trip, the breaker, what cause it to trip.

Circuit breaker trip after install of GFCI breaker [ 3 Answers ]

I'm replacing an outlet under kitchen sink that garbage disposer and dish washer were plugged into because they stopped working. The old outlet was not GFCI. So I'm attempting to replace it with one. Our home was built in the '50s and has no ground line yet. I used an extension cord to plug them...

20amp circuit breaker, 15 amp receptacles [ 2 Answers ]

I have a 20amp circuit breaker with 15 amp receptacles and light switches on #12 wire with a load of 1700, is this allowable? If not, and I change to a 15 amp circuit breaker, is the 1440 watt safety load in the code or is it a non-code safety suggestion?


View more questions Search