Ask Experts Questions for FREE Help !
Ask
    Badboyz01's Avatar
    Badboyz01 Posts: 1, Reputation: 1
    New Member
     
    #1

    Nov 23, 2013, 10:57 PM
    220vac Heater
    I have a heater that is a 220vac can I use it on a 120vac? I think it will but the heater elements will be at half heat.
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #2

    Nov 24, 2013, 11:49 AM
    Not quite that easy. When voltage is cut in half, amperage doubles assuming wattage stays the same. For example, if something draws 10 amps at 240 VAC, it will draw 20 amps at 120. Amps = watts /volts. If there is a fan in the heater, it will not function. Better to get a 120 heater or pull a 240 line.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #3

    Nov 25, 2013, 07:18 AM
    Additional information:

    The reason the amperage is important is because if the amperage is to high for the circuit, it could cause the conductors to get to hot. Or cause the breaker to trip as in a 15 amp circuit carrying a 20 amp load.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #4

    Nov 25, 2013, 08:12 AM
    Okay, the math behind the first response is incorrect.

    In a purely resistive circuit (such as a heater), reducing the voltage by half will reduce the amperage by half, not double it.

    To rephrase the first response; if a 240 volt 2400 Watt heater (2400W/240 Vac = 10 Amp) heater is reduced to 120 Volts, it would require 20 Amps at 120 volts to generate 2400 watts.

    To solve this properly, you must know the resistance of the heater coil. To get this, divide the Voltage, squared by the Wattage. (240*240/2400 = 24 Ohms)

    The device's resistance is not going to change because the voltage changes, so according to Ohm's law 120V/24 Ohms will generate a 5 ampere current.

    120V*5A = 600 Watts. So the max amount of Watts (heat) would be 600 Watts. The Wattage is reduced by a factor of 4.
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #5

    Nov 25, 2013, 03:29 PM
    Note I stated "assuming wattage stays the same".
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #6

    Nov 25, 2013, 04:00 PM
    Not a problem. Because the OP was using a specific heater, I just thought I could give a clearer answer by showing that the heat given off would drop considerably because the resistance of the heater stayed the same and the voltage dropped.

    No intent to offend.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

How can I wire 1-110vac and 1-220vac outlet on a 4 wire 220vac extension cord? [ 2 Answers ]

I have a 220vac 3 wire extension cord to which I wish to add a 110vac outlet as a convenience. Can this be done safely since there is no ground wire?

How to convert 220vac to 110vdc [ 2 Answers ]

I have a shunt release with 220vac power supply but actually the line power supply is 110vdc,what should I do?

Wiring for 220VAC - 30 Amp Motor [ 5 Answers ]

When doing the wiring in my new garage addition, I planned for a future two post cars lift. I failed to adequately check out the power requirement for said lift. I ran 3-#12 wire+ground wire from the sub-panel to the site about 30 ft away. Now I find that on all the lifts (so far) available, they...

Air conditioners 120vac vs 220vac [ 1 Answers ]

I want to purchase a window air conditioner. Some say that a 220 vac air conditioner is best, I want to know why. I understand that with the 220vac system, you can have more capacity, more BTU's. I don't need much since the room is small. What the difference?


View more questions Search