    Can a new 20 amp wall oven be wired to an existing 40 amp wire and breaker?
    The existing 8 gauge wire going to the breaker box cannot be changed (no access to box from attic). I guess the question is can the breaker itself be changed and if so, to a 20 or 30 amp?
    Hoot Jigger's Avatar
    Hoot Jigger Posts: 3, Reputation: 2
    New Member
     
    #2

    Nov 16, 2013, 07:26 PM
    Yes, you can downsize the breaker... the problems you may face are getting that #8 into the lug opening of a 20 amp breaker, I wouldn't use a 30 if the oven is rated 20. At the wall oven, depending on the termination box, the same problem may exist.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #3

    Nov 16, 2013, 08:08 PM
    Add a #12 pig tail to the end of the #8 and connect to breaker.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Is it OK to have 15 amp wire and a 20 amp breaker? [ 3 Answers ]

We're in the process of purchasing a house. The inspector says the 20 amp breaker with 15 amp wire is a fire hazard. The homeowner/seller, who's dad is a retired electrician, says it's fine. W'ere trying to determine if this needs to be addressed/changed or if it's OK to have 15amp wire with 20...

Wire gauge & breaker amp for A/C [ 3 Answers ]

Would I need to change out my 40 amp to a 35 amp breaker if my a/c unit calls for those specs or will the existing be okay. Oh yea 10G wire is in place now. I'm talking about a 3 ton heat pump split unit.

5.3 amp pump motor and 1500 watt wall heater on same 20 amp breaker [ 9 Answers ]

I want to wire a bath room up flush toilet which is 5.3 amps motor into a curicuit with a 1500 watt wall heater ( 13 amps) on a 120 -20 amp breaker . The heater is never on and the toilet would only come on when some one uses down stairs bathroom.

Replace 4 wire ceiling fan (& wall plate 2 wall sliders), with 5 wire fan + remote? [ 6 Answers ]

Hi all, Current configuration: Wall switch that has 2 sliders, one for the fan (has multiple speed capability) and the other for the light (has dimming capability). Our wall slider switch looks like this one (but not this make/model), just for FYI: Hunter Fan/Light Dual Slide Preset Control -...

Wire size wire & circuit breaker do I need for a 15.8 range [ 2 Answers ]

What size circuit breaker & wire size do I need rfor a 15.8 raqnge ?


View more questions Search