    Is a 40 amp service enough for a 38 amp hot tub
    A friend came over and claimed that a 38 amp hot tub should be on a 50 amp breaker, not the 4o amp that it is installed on. Logic dictates that he is wrong, but he claims it would have been more efficient and cheaper to run. Is he right?

    He also claimed that it should have been hooked up using 8-2 gauge wire and not 8-3.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #2

    Oct 22, 2013, 01:16 PM
    No, your friend doesn't know what he is talking about.
    Circuit breaker is determined by the amperage draw and the size of the conductors. Efficiency doesn't enter the picture.
    Eight (8) is the size of the conductors, two (2) or three (3) is the number of conductors. You cannot increase the size of the breakers without increasing the size of the conductors. Whether the hot tube is 240 volts or 120/240 volts determines the number of conductors.
    drtom4444's Avatar
    drtom4444 Posts: 3,282, Reputation: 145
    Ultra Member
     
    #3

    Oct 23, 2013, 11:06 AM
    I hope you used 8-2 with ground because you need a minimum of 3 wires for a 240 volt service. The size of the breaker does not matter; it's the size of the wire that is important. The breaker is there to protect the wires from burning up and causing a fire or causing damage to the equipment, too. What you have is fine.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Can I add a 60 amp GFI (for new hot tub) to my 100 amp service panel? [ 1 Answers ]

I bought a used hot tub. It comes with a 60 amp gfi switch. My home has 100 amp panel. I presently have 5 small pony boxes off the main panel. It is old style glass screw in fuses. House built in '68. Can I just add another pony box rated for 60 amp fuses ? If not, do I then need to rewire...

Can I add a 50amp Hot tub to 100 amp service [ 1 Answers ]

100 amp service 100 amp main. Enough space to add adequate breaker. But need to know if load calculations are within code. Home has 1200 sq ft of living space. 1 30amp electric dryer circuit NOT USED. Gas Dryer, Gas Water Heater. Electric Range on 50 amp breaker. Central air on 40 amp breaker. 6 15...

Can a 40 amp hot tub handle a 60 amp breaker [ 0 Answers ]

I am going to wire an older hot tub it is a sweetwater lx-15 model the control panel in the tub says 24/40 amps do I need a 40 amp breaker at the main box and a 40-60 gfci outside or can I use a 60 amp in the basement at the main box the tub has two(2) pumps and a 5.5 kw heater thanks for any...

400 amp service, 2 200 amp panels, 320 amp meter socket [ 10 Answers ]

Hi, this is my first post here, but I have been reading a lot and have already learned a bunch. I want to thank TK already and hope you reply to this. I am in the process of designing my electrical system for my new home. I have some electrical experience, but am by no means a pro. I am...

400 amp service with 2-200 amp panels & 320 amp socket [ 6 Answers ]

Hi TK. I am running 400 amp service into my new contruction home. The electric compnay is running a single 400 amp line to the meter. I have to split it to the two panels at that point. You had told me once before that I need a 320 amp meter socket and then run 2-200 amp lines to the separate...


View more questions Search