    High side low side r22 same pressure when off?
    I have a chiller that uses r22. It is water cooled and cools water to 55 deg. Problem. First the high and low sides are both at 120 in the water bath and room temp around 72 deg. So this may be normal for this situation but, when I start the unit the high side goes to 450 psi in about 15 seconds and the low side will go up to 175 psi. I'm leaning to a plugged cap tube but the low side puzzles me. I have been reading where they say the condenser is not shedding the heat but the condenser is water cooled and I have a flow meter on the line to verify it is flowing and cooling the condenser. Any ideas?
    Grady White's Avatar
    Grady White Posts: 1,417, Reputation: 59
    Ultra Member
     
    #2

    Oct 15, 2013, 08:22 PM
    The condenser coils could be so heavily coated with mineral deposits they can't transfer heat. What are your water inlet & outlet temperatures for the condenser?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Dodge stratus air conditioning high side has low and low side has high pressure how [ 0 Answers ]

Our dodge stratus 2001 air was cooling and then not cooling then cooling again Took it to our mechanic he said he did not know how to repair. The compressor was good, but the high pressure line is now low pressure, and the low pressure has highest pressure, he said he did not know what was causing...

The high pressure side and low pressure side of my ac unit are at 115 lbs, what do I [ 4 Answers ]

I have a Goodman ac unit at my house,the high pressure side and low pressure side are equal at 115 lbs. How do I solve this problem, or what do I do to fix this problem.

Low side pressure reading be on an r22 home unit [ 1 Answers ]

I have a Goodman natural gas pac unit 13 seer , what should the pressure gauges be reading on the low side mine is currently running around 70 to 72 which reflects to 33 to 34 degree coil temp is this about right.

R22 LOW SIDE and high side same pressure 120psi [ 2 Answers ]

r22 LOW SIDE and high side same pressure 120psi. Condensing unit works for 15 seconds and then stops

Do you add 30 410a freon pressure like you do r22 and r12 for high side pressure in c [ 1 Answers ]

Do you have to add 30 to the ambeint air temp. like you do for r22 and r12 to R410a freon to get the proper high side pressure reading


View more questions Search